Temperature inputs not reading the correct value
  • Temperature inputs not reading the correct value
  • ScottLeedberg
    ScottLeedberg
‎2018-09-06 02:15 PM
Temperature inputs not reading the correct values
  • Cyberstation
  • IOUs
  • Controller
Bad input
Bad controller
Bad sensor
Replace sensor with a 10k ohm resistor.  Temperature input should read roughly 77°F or 25°C.  If it does then the problem is with the sensor.  If it does not then the problem is either with the input board or that particular input itself.