Preparing LonWorks Configurations for Upgrade - LonWorks Pre-Upgrade - Links to Workstation Only hotfixes.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Preparing LonWorks Configurations for Upgrade - LonWorks Pre-Upgrade - Links to Workstation Only hotfixes.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4545 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Preparing LonWorks Configurations for Upgrade - LonWorks Pre-Upgrade - Links to Workstation Only hotfixes.

Picard Product_Support
‎2018-09-10 10:43 AM

Last Updated: Crewman ContentModerator ‎2025-09-19 02:56 AM

Issue

Preparing LonWorks Configurations for Upgrade

You use this procedure when you want to prepare LonWorks configurations for a
version 1.5.x upgrade, a version 1.6.x upgrade, or a version 1.8.x upgrade to a final 1.9.X or Higher version.

WorkStation ONLY hotfixes are needed to Prepare the LonWorks configuration in order to upgrade to an SBO system 1.9.X or higher.

Links to locating hotfixes on Exchange are needed.

Product Line

EcoStruxure Building Operation

Environment

  • SBO Workstation Hotfix Only v1.5.0.17121
  • SBO Workstation Hotfix Only v1.6.2.1220
  • SBO Workstation Hotfix Only v1.7.2.11111

Note: AS-P HW.62 required for a LON system with a minimum SBO Software revision at 1.7.2.X

Note: For Systems that are running SBO Software Revision 1.8.X please follow TPA-SBO-17-0002.00 -Server with LonWorks devices - Important software update - TPA-SBO-17-0002.00

Cause

Difficulties experienced in locating these files on the Exchange.

Resolution

Prepare LonWorks Systems Running Version 1.5, 1.6, or 1.7.

For Systems that are running SBO Software Revision 1.8.X please follow TPA-SBO-17-0002.00 - Server with LonWorks devices - Important software update - TPA-SBO-17-0002.00

SBO Workstation Hotfix v1.5.0.17121 - Contact Country Level PSS

SBO Workstation Hotfix v1.6.2.1220 - Contact Country Level PSS

SBO Workstation Hotfix v1.7.2.11111- Link

To prepare LonWorks configurations for upgrade via the WorkStation Only Hotfix:

Bring the system up to the base version within your respective site to SBO V1.5, 1.6.2, or 1.7.2. Then apply the WorkStation Only Hotfix from the list above to your respective version.

1. In WorkStation, in the System Tree pane, select the EcoStruxure BMS
server you want to prepare for the upgrade.

2. On the File menu, point to LonWorks and click Pre-upgrade LonWorks
configuration.

3. Click Next.

4. Click Finish.

NOTE: Any EcoStruxure BMS that is currently at 1.8 or higher can be upgraded directly
to 3.1 with one added note,  if the system has LON it will need to go through the LonWorks Pre upgrade before you can upgrade to 1.9.X or HIGHER. If you are upgrading from a version that is older than 1.8, read the
documentation that describes the upgrading process for the relevant version.

Upgrade Path as of 3.1.PNG

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • 19205
  • JonathanHernandez20
  • PeterLarsen20
Was this article helpful? Yes No
50% helpful (1/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore