Serial connection to I/A Series G3 ENC serial system shell using Windows HyperTerminal

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Serial connection to I/A Series G3 ENC serial system shell using Windows HyperTerminal
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
9861 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Serial connection to I/A Series G3 ENC serial system shell using Windows HyperTerminal

Picard Product_Support
‎2018-09-10 02:56 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:07 AM

Issue

Serial connection to I/A Series G3 ENC serial system shell using Windows HyperTerminal

Product Line

TAC IA Series

Environment

  • I/A Series G3 Enterprise Network Controllers:
  • ENC-410-1
  • ENC-410-1-N
  • ENC-520-2
  • ENC-520-2-N

Cause

There maybe a need to access the ENC via its serial port if the IP address of the ENC is unknown or for troubleshooting purposes when the ENC's Ethernet port is not functioning.

Resolution

Hardware required for connection to ENC's RS-232 port:

  • 8-conductor flat silver satin stranded cable with standard male (plug) RJ-45 connectors.
  • RJ-45 to DB-9 adapter (part number: UNCC-405) or a socket-to-plug type RJ-45 to DB-25 adapter (part number: UNCC-430).
  • A functioning COM port on your computer.
  • A 2-pin jumper for connection to the ENC's 'Mode' connector.

Refer to the Installations Instructions for ENC-410 (pages 10 & 11) or ENC-520 (pages 10 & 11) for details on the cable and adapter.  Pinout configuration for a RJ-45 to DB-9 Null Modem Adapter (part number UNCC-405) used for serial i... also refers to these pin outs.

Connection to ENC's serial system shell using Windows HyperTerminal (for operating systems without HyperTerminal, please refer to Hyperterminal on Microsoft Windows Operating Systems😞

  1. Connect the cable and adapter between the ENC’s RS-232 port and the RS-232 COM port you are using on your computer.
  2. Start HyperTerminal (Programs > Accessories > Communications > HyperTerminal).
  3. In the 'Connection Description' dialog, type a name for this session. For example, 'Connection to ENC'. Click OK.
  4. In the 'Connect to' dialog, use the 'Connect using' drop-down list to select the COM port you are using on your computer. Click OK.
  5. In the Com(n) Properties dialog, choose the following settings:
    Bits per second: 57600
    Data bits: 8
    Parity: None
    Stop bits: 1
    Flow control: None
    Click OK.
  6. On the ENC circuit board, locate the 4-pin Mode connector and put a 2-pin jumper on the 2 outer pins. Refer to page 7 of the ENC-410 or ENC-520 Installation Instructions for position of the Mode connector.
  7. With your HyperTerminal session active and configured to log to a file, remove power from the ENC, let it cycle down, then reapply power.  The easiest way to power cycle the ENC is to unplug the 6-pin power plug from the circuit board, wait 15 seconds and plug it back in.  After some number of seconds, text should appear in the HyperTerminal window similar to:
    Press any key to stop auto-boot...
  8. Do not press any key, wait for the login prompt. If you did press a key to stop auto-boot, select option 1.
  9. At the login prompt, enter the platform user name, and at the password prompt, the platform password. The default user name is 'tac' and password is 'niagara'. The system shell menu should now appear. You should able to see the IP address of the ENC now.
  10. When finished using the serial system shell, do the following:
    • Remove the 2-pin jumper from the Mode connector of the ENC.
    • From the system shell menu, select the Reboot option. Type 'y' at the 'Are you sure you want to reboot [y/n]' prompt, and press Enter. Shutdown-related text appears in the HyperTerminal window, and then the connection is dropped.
  11. Press the Disconnect button on the HyperTerminal tool bar.
  12. Exit from the HyperTerminal application, selecting to Save if you wish to reuse this HyperTerminal setup for future connection to an ENC.

If you are troubleshooting the ENC, send the HyperTerminal start up messages to Product Support for analysis.

Labels (1)
Labels:
  • TAC IA Series
Attachments
Tags (1)
  • Find more articles tagged with:
  • 5623
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore