SMTP Email Alarm Configuration in Continuum 2.0 and 2.03

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • SMTP Email Alarm Configuration in Continuum 2.0 and 2.03
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
6884 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

SMTP Email Alarm Configuration in Continuum 2.0 and 2.03

Picard Product_Support
‎2018-09-11 09:08 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:57 AM

Issue

Instructions are needed to configure the new SMTP configuration.

Product Line

Andover Continuum

Environment

  • Continuum
  • Non-Microsoft Exchange/Outlook SMTP Email

Cause

Configuration for the SMTP Configuration for email alarming in Continuum 2.00 through 2.03

Resolution

In Cyberstation 2.0 and above, you no longer need Microsoft Outlook and Exchange to send email alarm notifications. Other SMTP servers can be used on the network and other email clients can be used also to send email alarm notifications directly to an intended recipient.

Note:

Public SMTP servers such as Gmail SMTP and Yahoo SMTP do not currently work with this solution as they require SSL or certain unsupported port combinations. The connections these servers establish cause connection issues within the SMTP application. Private SMTP (In-house) servers can be set up and used.

 

Steps to Configure SMTP Email Alarming

 

  1. Open and Event Notification

    OpenEventNot.png

  2. Navigate to the Actions Tab

    Select which events to receive email alarms

    EventNotActions.png

  3. Select the Delivery Tab
    1. Click the Add Recipient button to open the recipient configuration

      EventNotRecipient.png

    2. Browse for the recipient Cyberstation by click the ellipsis

      EventNotBrowseRecipient.png

    3. Select the recipient Cyberstation

      EventNotSelectRecipient.png

  4. Select the SMTP Configuration button in the Recipient Configuration window

    SMTPConfigureButton.png

  5. Fill in the Server Configuration fields in the SMTP Configuration window
    1. Specify the SMTP Server address, port and login information

      SMTPConfigureFields.png

    2. Fill in the Email Configuration

      Specify the sender's email address - this is the email address the email will be sent from and it is also the email address that failed emails will be sent to

       

       Type in a Subject line if needed or the default Continuum email subject line will be used

      EmailConfiguration.png

    3. Alarm Option Settings - Fill in the RetryCount and Retry Time fields

       Retry Count - once you pass this value the email is dropped. The maximum Retry Count is 10

       Retry Time -  field is in minutes. The maximum is 1440 minutes (24 hours)

      Options.png

  6. Adding an email address to the recipient list
    1. Click the Display Master List to open the SMTP Master Email Configuration Dialog

      SMTPConfigDisplayMasterList.png

    2. Place a check in the check box to add an email address from the existing Master List to the Event Notification's recipient list and then click OK

      MasterEmailConfiguration.png

  7. Adding or deleting email addresses from the Master Email list
    1. Open the SMTPMasterEmail Event Notification in the templates folder

      MasterEmailNotification.png

    2. In the opened SMTPMasterEmail Event Notification click the Display Master List button

      SMTPConfigDisplayMasterList.png

    3. Click the Add Recipient or Delete Recipient button depending on what is needed

      MasterAddDeleteButtons.png

    4. After selecting Add Recipient supply the email address in the recipient field and click Add Recipient

      AddRecipient.png

    5. After selecting Delete Recipient, select the address to highlight it and then click the Delete Recipient button. Multiple Selection is supported

      DeleteRecipient.png

    6. To deliver email notifications to the added email address, select the check box next to it

      EmailDeliveryCheckBox.png

  8. Testing to ensure email address recipients receive emails
    1. Select the address you wish to test and click the Test Selected button

      TestSelected.png

    2. Successful email to SMTP Server test will display a pop-up

      EmailTestSuccess.png

    3. Failed email to SMTP server test will display a pop-up to the Sender's email address

      EmailTestFail.png

    4. Final address configuration

      FinalConfigOK.png

  9. Recipients Configuration Options
    1. Place a checkmark next to the option needed Ex. Primary or Backup  SMTP Email
    2. A checkmark next to Repeat. Repeat will function as if it were an Outlook email alarm and send until the alarm is acknowledged.

      RecipientsConfigOptions.png

Known issues:

In order for BACnet controllers to use the new SMTP feature, the following hotfix from the following link is needed. 

CyberStation v2.00 (Only) SMTP Emailing & BACnet Alarms - Hotfix

2.03 contains the hotfix listed above

 

For additional information, see the Cyberstation Help, search for SMTP.

Labels (1)
Labels:
  • Andover Continuum
Tags (10)
  • Find more articles tagged with:
  • 16848
  • AlanWood22
  • alarm
  • alarms
  • DavidShore21
  • email
  • email alarm
  • exchange
  • outlook
  • smtp
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore