No license after reboot when TAC Vista Server (TACOS) runs as a service

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • No license after reboot when TAC Vista Server (TACOS) runs as a service
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3941 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

No license after reboot when TAC Vista Server (TACOS) runs as a service

Picard Product_Support
‎2018-09-11 01:10 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:03 AM

Issue

After rebooting the PC, TAC Vista Server (TACOS) doesn't get a license. You need to restart TACOS after each reboot to get a license.

Product Line

TAC Vista

Environment

  • TAC Vista License Server
  • TAC Vista Server

Cause

TAC Vista Server (TACOS) starts up before the license system is ready to serve licenses, and therefore everything is offline until you restart TACOS.

Resolution

Download these tools

TAC Vista Run Mode

TACLicenseServer Settings (only for TAC Vista 5.1.8 and later)

First of all, make sure that you have a system that is working normally and has the appropriate default settings. For more information, watch this video on YouTube

Make the following setting in TACLicenseServer Settings

[1] Set the startup type to "Automatic" and the taclic port to 2170

01_TACLicenseServer settings.png

[2] Click the "License Setup" button, and write the name or IP address of the local PC. Don't use "localhost" or 127.0.0.1 but the actual name or IP.

02_0_TACLicenseServer settings.png

 02_TACLicenseServer settings.png

[3] Click the "License Files" button, and check that only valid license file(s) is present in the license files folder - no other files can be in this folder.

03_TACLicenseServer settings.png

04_TACLicenseServer settings.png

[4] Start the license server

05_TACLicenseServer settings.png

Make the following setting in TAC Vista Run Mode

[1] Enter the username and password of a user with local administrator rights that have at some point been logged in on the PC. LocalSystem can be used, but it is not recommended.

01_TAC Vista Run Mode.png

[2] Set TACOS to run as a service

02_TAC Vista Run Mode.png

[3] In "Service Tools" set the service to start type "Automatic Delayed"

03_TAC Vista Run Mode.png

[4] Start the service

05_TAC Vista Run Mode.png

Now reboot the PC

If TACOS still doesn't get a license after a reboot, try making this additional setting in TAC Vista Run Mode

[1] Stop the service

06_TAC Vista Run Mode.png

[2] Make the service depend on the license server, and also the Loytec driver if it is used in the system.

04_TAC Vista Run Mode.png

Now reboot the PC

If TACOS still doesn't get a license after a reboot, try adding this environment variable to Windows

[1] Open the properties for the computer (Click the Windows start button, right-click "Computer", click "Properties")

[2] Click on "Advanced system settings"

Advanced System Settings.png

[3] Add a new system variable called "TCP_NODELAY" and give it the value 1

Environment Variable.png

Now reboot the PC

If TACOS still doesn't get a license after a reboot, contact Product Support Services and reference this article

Now reboot the PC

If TACOS still doesn't get a license try making this additional setting in TAC Vista Run Mode

Now reboot the PC

If TACOS still doesn't get a license try making this additional setting in TAC Vista Run Mode

Labels (1)
Labels:
  • TAC Vista
Attachments
TAC Vista Run Mode.zip
TACLicenseServer Settings.zip
Tags (2)
  • Find more articles tagged with:
  • 17394
  • RandyDavis22
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore