Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

I/A Series (Niagara) R2 Windows Compatibility Matrix

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/A Series (Niagara) R2 Windows Compatibility Matrix
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3631 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/A Series (Niagara) R2 Windows Compatibility Matrix

Picard Product_Support
‎2018-09-10 04:23 AM

Last Updated: Crewman ContentModerator ‎2025-10-10 02:54 AM

Issue

Is the I/A Series R2 software compatible with a specific version of Windows?

Product Line

TAC IA Series

Environment

  • I/A Series (Niagara) R2 software
  • Windows 32-bit operating system

Cause

Only specific releases of the I/A Series R2 software have been certified compliant with specific versions of the Microsoft Windows software. 

Resolution

The following chart details the version compatibility between the releases of the I/A Series R2 software and the various 32-bit versions of the Microsoft Windows Operating System software. 

NOTE: I/A Series R2 software cannot be installed directly in any 64-bit version of the Microsoft Windows Operating System.
Virtual platforms such as VMware Server 2 or Microsoft Virtual Server 2008 are not supported in R2.

  R2 522 R2 527 R2 529 R2 532 R2 535 R2Tunnel Clients TunnelAX Clients  VAS
2.50
VAS 3.92
                   
Windows XP Professional (SP3) (32-bit) Y Y Y Y Y Y Y Y Y
Windows XP Professional (SP3) (64-bit) N N N N N N N N N
                   
Windows Vista Business / Enterprise / Ultimate  (SP2) (32-bit) N Y Y Y Y Y N N N
Windows Vista Business / Enterprise / Ultimate  (64-bit) N N N N N N N N N
                   
Windows Server 2003 Standard  / Enterprise (SP2) (32-bit) Y Y Y Y Y Y N N N
Windows Server 2003 Standard  / Enterprise (SP2) (64-bit) N N N N N N N N N
Windows Server 2003 R2 Standard  / Enterprise (SP2) (32-bit) Y Y Y Y Y Y N N N
Windows Server 2003 R2 Standard  / Enterprise (SP2) (64-bit) N N N N N N N N N
                   
Windows Server 2008 Standard  / Enterprise (SP2) (32-bit) N N N N N N N N N
Windows Server 2008 Standard  / Enterprise (SP2) (64-bit) N N N N N N N N N
Windows Server 2008 R2 Standard  / Enterprise (SP2) (32-bit) N N N N N N N N N
Windows Server 2008 R2 Standard  / Enterprise (SP2) (64-bit) N N N N N N N N N
                   
 Windows Server 2012 (All Versions 32-bit & 64-bit) N N N N N N N N N
 Windows Server 2012 R2 (All Versions 32-bit & 64-bit) N N N N N N N N N
                   
Windows 7 Professional / Enterprise / Ultimate (32-bit) N N Y* Y* Y* Y* Y* N N
Windows 7 Professional / Enterprise / Ultimate (32-bit) (XP-Mode) N N Y* Y* Y* Y* Y N N
Windows 7 Professional / Enterprise / Ultimate (64-bit) N N N N N N N N N
Windows 7 Professional / Enterprise / Ultimate (64-bit) (XP-Mode) N N Y* Y* Y* Y* N N N
                   
VMWare Server (all versions) N N N N N N N N N
Microsoft Virtual Server (all versions) N N N N N N N N N
                   
Microsoft SQL Server 2000 Y Y Y Y Y        
Microsoft SQL Server 2005 N Y Y Y Y        
Microsoft SQL Server 2008 N N N N N        
Microsoft SQL Server 2008 R2 N N N N N        

* Refer to PA-00163 for Windows 7 Support Info.

NOTE: When selecting a computer on which to install the I/A Series R2 software, select one that meets or exceeds the recommended hardware for the selected operating system.

For the larger Schneider Electric BMS offering please refer to Software and Firmware compatibility matrix for older versions of I/NET, Vista, Andover Continuum, Sa...

Labels (1)
Labels:
  • TAC IA Series
Attachments
Tags (1)
  • Find more articles tagged with:
  • 6369
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore