I/A Series G3 Modbus TCP communications to Siemens Moore 353 controller stops updating after a period of time after ENC/JACE reboot or station start.
  • I/A Series G3 Modbus TCP communications to Siemens Moore 353 controller stops updating after a period of time after ENC/JACE ...
‎2018-09-06 11:24 AM
Last Updated: Crewman ContentModerator ‎2025-09-25 02:46 AM
I/A Series G3 Modbus TCP communications to Siemens Moore 353 controller stops updating after a period of time after ENC/JACE reboot or station start.  The controllers do not drop offline and the associated Modbus proxy points no longer appear to update.
I/A Series G3, Modbus TCP 3.6.47 and lower
Modbus TCP transaction Identifiers are used to associate the future response with the request.  The transaction ID is a two byte value that can range between 0 and 65535. The Siemens Moore 353 controller appears unable to process Modbus transaction IDs at or higher than 1024.
The I/A Series G3 Modbus TCP driver has been modified to allow the configuring of the maximum transaction ID for each device.
  1. Download the following modules from The Exchange Download Center:
    • modbusCore-3.6.47.1.zip
    • modbusTcp-3.6.47.1.zip
  2. Install to the appropriate I/A Series G3 Workbench modules folder and upgrade the modules in the ENC/JACE.
  3. Modify the transaction ID to a value lower than 1024 and reboot the ENC/JACE station.
  • TAC IA Series
  • 10888