How to setup automatic table truncation on Single-User SQL Express systems

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to setup automatic table truncation on Single-User SQL Express systems
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2127 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to setup automatic table truncation on Single-User SQL Express systems

Picard Product_Support
‎2018-09-10 10:05 PM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:37 AM

Issue

How to setup automatic table truncation on Single-User SQL Express systems.

Product Line

Andover Continuum

Environment

  • Continuum Cyberstation
  • Single-User
  • SQL Express
  • SQL Server 2005

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance.

Cause

Only the ExtendedLog table is automatically truncated on an Single-User SQL Express Continuum system. The other tables that can fill up quickly and need to be truncated regularly are not catered for (accessevent, activityevent, alarmevent, and errorevent).

Resolution

IMPORTANT: Make sure to perform a full SQL Database backup before attempting to make any changes to the database. (See Move / Backup / Restore a database on a Single User SQL2005 Express system for details on how to backup your database and, if not already installed, where to get Management Studio from)

Use the attached file SQLExpress to add table truncations.zip, to configure your Single-User SQL Express system to automatically truncate these tables when it does the ExtendedLog truncation. After downloading the file, follow the steps below.

  1. There are three files in the archive, these need to be copied to your Continuum folder on your Single-User system running SQLExpress as the database engine.
    • LogTruncate.SQL
      This file is the SQL script that performs the truncation of the four tables (accessevent, activityevent, alarmevent, and errorevent) to the number of days you specify - I have selected 90 days as my default but you can change this to whatever you require for each table.
    • CS_LogTruncate_OneOff.bat
      This batch file will run the LogTruncate.sql script once when manually executed. You will need to change the server name "PC3" to whatever your PC's name actually is on your system.
    • CS_Hrly - with LogTruncat.bat
      This is the batch file that will be renamed and replace the existing "CS_Hrly.bat" file currently located in your Continuum folder. This is the same as your current file except it has added the LogTruncate.sql script so that this will now be executed every hour along with the rest.
  2. Backup "CS_Hrly.bat" file in Continuum folder by renaming the file to something like "CS_Hrly ORIGINAL.bat".
  3. Rename "CS_Hrly - with LogTruncat.bat" to "CS_Hrly.bat", copy into (overtop the existing file if you haven't renamed it) the Continuum folder, and change the server name "PC3" to your PC's name. This should now execute this table truncation script along with the other database maintenance scripts every hour.
Labels (1)
Labels:
  • Andover Continuum
Attachments
SQLExpress to add table truncations.zip
Tags (2)
  • Find more articles tagged with:
  • 8199
  • sql2005
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore