Extended Elevator control (Step by step instructions)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Extended Elevator control (Step by step instructions)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • SESA128071
    SESA128071

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
2 Likes
2378 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Extended Elevator control (Step by step instructions)

Picard Product_Support
‎2018-09-07 01:13 AM

Issue

Extended Elevator control (Step by step instructions)

Product Line

TAC INET

Environment

  • I/NET Seven
  • DPU Firmware 3.20 or above. (DPU7920 with 48k MIP or SCU1284)

Cause

Extended elevator control allows support up to 79 floors and easier programming methodology than the traditional method.  This has been added to I/NET Seven software and DPUs as detailed in the environment. 

Resolution

To use any of these features requires that the DPU be a 7920 w/ MIP board or the new SCU1284. 7910 and 7920 w/o MIP board will still work with the I/Net system but they cannot use these functions. The host prevents the download of these features to any DPU revision prior to 3.10.

 

Extended Elevator Control Setup Example

This is based impart on basic prior knowledge of InetSeven Host software setup and configuration to include but not limited to Controller Station Parameters, Resident I/O, Point Extensions, Operations of Network Configuration, and Access Configurations (Doors, Tenants, Groups, Individuals and Personnel Schedules).

Hardware required: DPU 7920 48k (The following control will only apply to the 7920 48k)

Please follow these steps to configure extended elevator control.

Resident I/O Editor

  1. Edit / Controller / Resident I/O – Add the following
    • Internal DO Door Reader point
    • Internal DI point for each Floor DO
    • External DO point for each Floor button DI

Note – Save Door in the Network Configuration editor.

Controller Door Editor

  1. Edit / Controller / Door Editor
  2. Select Door to add Elevator Control
  3. Modify – check Elevator Control box
  4. Select “Message type” Alarm / Transaction

Note – Ensure a Schedule (s) has been assigned to the Door reader point.

Controller Elevator Parameter

  1. Edit / Controller / Elevator
  2. Add Elevator Extension to reader point.
  3. Add Floor parameters.
  4. Complete the following;
  5. Floor Index Selection
  6. Floor designation
  7. Button Enable (DO)
  8. Button Selection (DI)

Note – When finished “STOP” Do not select floors, Select OK and Close.

Network Configuration 

  1. Edit / Host Computer / Network Configuration.
  2. Penetrate down to the DPU (Door Read Point) with Elevator Control
  3. Penetrate one more level and SAVE all your floor extensions.

Tenants

  1. Access / Tenants
  2. Select Tenant
  3. Locate Door Reader point – Remove “X” (Unselect).
  4. Place an “X” next to all floors that tenant will have access to – Select Ok
  5. At this time I would suggest performing a save function followed by an SLI and DPU restore.

Individual Editor

You are now ready to add individuals or assign individuals access to floors.

Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 1767
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore