Issue
Should managed switches be set to half duplex or full duplex?
Prorduct Line
Andover Continuum
Environment
Continuum Cyberstation
2nd Generation Controllers
- BCX 4040, 4000, 9640
- NC2 9680
- ACX 5740, 5720
1st Generation Controllers
- CMX 9924
- CX 9900, 9901, 9940
Cause
Configuration for managed switches.
Resolution
Most sites will have managed switches set for Auto Sensing 10/100
For sites that must use a designated configuration, our 1st generation controllers communicate 10 half duplex while the 2nd generation controllers communicate 100 full duplex.