Cannot delete Continuum personnel profiles
  • Cannot delete Continuum personnel profiles
  • Dave_Shore
    Dave_Shore
‎2018-09-06 02:00 PM
Cannot delete personnel profiles from personnel manager.
Andover Continuum
Continuum 1.81
Personnel profiles have become corrupted and can not be deleted. You can not rename areas without removing/replacing them in the profile.
Procedure to remove corrupted personnel profiles:
  1. Start Continuum
  2. Run ACDEVApp.exe from the Continuum directory.
  3. Click Generate.
  4. Replace the 3 lines:
    <REQUESTOPERATIONS>
    </REQUESTOPERATIONS>
    </IACDEVREQUEST>
    ... with the following 6 lines, only replace the word ProfileName with the name of the profile being deleted:
    <REQUESTOPERATIONS>
    <DELETE>
    <OBJECT PATH="ProfileName"/>
    </DELETE>
    </IACDEVREQUEST>
  5. Press the "Process Request" button
  • 4826
0% helpful (0/1)