Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Niagara R2/G3 UNC/JACE reboots every 15 minutes with "Battery test failed" logged

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Niagara R2/G3 UNC/JACE reboots every 15 minutes with "Battery test failed" logged
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Kim_Baze
    Kim_Baze
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2468 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Niagara R2/G3 UNC/JACE reboots every 15 minutes with "Battery test failed" logged

Picard Product_Support
‎2018-09-06 02:56 PM

Issue

A Niagara R2/G3 UNC/JACE is rebooting every 15 minutes and the standard output window indicates AC Power status failed and a "Battery test failed" gets logged as well.

Product Line

TAC IA Series

Environment

I/A Series UNC, ENC or JACE chassis with Gel-cell backup battery

Cause

Marginal or failed battery or bad battery charging fuse

Resolution

The UNC automatically performs a battery load test every 15 minutes. If the voltage drops below a predefined value, the battery test indicates "battery test failed". If the voltage is higher than the predefined value, the battery test indicates "battery test passed". This message is only reported once unless the detected battery condition changes.

A station alarm is generated only when the new outcome is different that the previous test. If a battery is marginal, the test may alternate between "passed" and "failed." Additionally, a bad or marginal battery has been known to cause random UNC reboots.

Begin troubleshooting by checking the battery fuse (field replaceable only in the UNC-500/510 controllers), connections and voltage level.  If the battery voltage is low (less than 12 Vdc), disconnect the battery and monitor the UNC for errors or rebooting. If the errors or rebooting stops install a new battery.  After installing the new battery, measure the battery charging voltage.  The voltage reading should be between 13 and 14.5 volts DC if a good battery is connected.  If the installed battery is partially discharged, the charging voltage reading may be as low as 12.5 volts.

In release 2.301.522, a change was made to how embedded controllers (UNC-410 / 500 / 510 / 520) perform the backup battery test.  Formerly, a "marginal" battery might result in continuous reboots. Now, the battery test is better coordinated with the AC power test. This prevents the scenario of repeated AC power fail shutdowns upon boot up if the battery is bad or weak.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 2681
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.