Temp Sensor for Class 1 Div 2 location

Intelligent Devices Forum

Schneider Electric support forum about all Intelligent Field Devices brands of Sensors, Thermostats, Glass Touch Panels, Valves and Actuators

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Intelligent Devices
  • Intelligent Devices Forum
  • Temp Sensor for Class 1 Div 2 location
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
CraigEl
Administrator CraigEl Administrator
42
MikaelKrantz
Kirk MikaelKrantz Kirk
11
Gary
Gary Schneider Alumni (Retired)
11
View All

Recommended Forums

  • SmartConnector Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Intelligent Devices Forum
Start a Topic
Solved
arlena
Lieutenant | EcoXpert Master arlena Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2023-03-16 12:02 PM . Last Modified: ‎2023-03-16 02:25 PM

0 Likes
4
2472
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-16 12:02 PM . Last Modified: ‎2023-03-16 02:25 PM

Temp Sensor for Class 1 Div 2 location

Can a 10K thermistor be installed in a class 1 div 2 location?  Or are there other sensor/transmitter combinations that could be installed in this environment?

It would be wired to an MPx controller outside the location.

 

Labels
  • Labels:
  • Temperature Humidity & Air quality Sensors
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
dano_
Lieutenant dano_ Lieutenant
Lieutenant

Posted: ‎2023-03-17 03:08 AM

1 Like
0
2441
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-17 03:08 AM

Hi, you should search for an "intrinsically safe temperature transmitter", as "Class 1 Div 2" describes presence of explosive atmosphere where sensor should be installed. In EU ATEX zone 2 area. as my information there are no such offered by SE.  (its not case of sensor characteristic, its about construction of a sensor, and barrier to prevent no electric spark can appears)   

just like for example https://www.tc-atex.com/uk/

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Troy_Wecker
Lieutenant JG Troy_Wecker Lieutenant JG
Lieutenant JG

Posted: ‎2023-03-17 09:57 AM . Last Modified: ‎2023-03-17 10:01 AM

1 Like
1
2427
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-17 09:57 AM . Last Modified: ‎2023-03-17 10:01 AM

A 10K thermistor itself does not act as a source of ignition.  There is no dynamic contact points or switching.

If the thermistor is part of a transmitter assembly,  then that product must be approved as suitable.  Typical Building Automation Sensors won't have that approval.

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

arlena
Lieutenant | EcoXpert Master arlena Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2023-03-17 12:46 PM

In response to Troy_Wecker
0 Likes
0
2422
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-17 12:46 PM

I  was more concerned about the input terminals of the controller (in this case an MPV).  I'm not sure of how much energy the controller input terminals are capable of supplying, but at any rate I think the controller would have to carry some type of rating or marking to make the AHJ happy.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

ezgod87
Crewman ezgod87
Crewman

Posted: ‎2023-04-07 04:39 AM

0 Likes
0
2329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-07 04:39 AM

For a school project I'm asked to design a temperature sensor with transistors exclusively.

I need to use the characteristics of a temperature-dependent transistor and implement a transistor(s) amplifier which will fix the sensitivity of the sensor.

I can only use bipolar and FET transistors, resistors and a continuous power supply +/- 15V.

router login 192.168.l.l

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
dano_
Lieutenant dano_ Lieutenant
Lieutenant

Posted: ‎2023-03-17 03:08 AM

1 Like
0
2442
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-17 03:08 AM

Hi, you should search for an "intrinsically safe temperature transmitter", as "Class 1 Div 2" describes presence of explosive atmosphere where sensor should be installed. In EU ATEX zone 2 area. as my information there are no such offered by SE.  (its not case of sensor characteristic, its about construction of a sensor, and barrier to prevent no electric spark can appears)   

just like for example https://www.tc-atex.com/uk/

Reply

Link copied. Please paste this link to share this article on your social media post.

Troy_Wecker
Lieutenant JG Troy_Wecker Lieutenant JG
Lieutenant JG

Posted: ‎2023-03-17 09:57 AM . Last Modified: ‎2023-03-17 10:01 AM

1 Like
1
2428
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-17 09:57 AM . Last Modified: ‎2023-03-17 10:01 AM

A 10K thermistor itself does not act as a source of ignition.  There is no dynamic contact points or switching.

If the thermistor is part of a transmitter assembly,  then that product must be approved as suitable.  Typical Building Automation Sensors won't have that approval.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

arlena
Lieutenant | EcoXpert Master arlena Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2023-03-17 12:46 PM

In response to Troy_Wecker
0 Likes
0
2423
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-17 12:46 PM

I  was more concerned about the input terminals of the controller (in this case an MPV).  I'm not sure of how much energy the controller input terminals are capable of supplying, but at any rate I think the controller would have to carry some type of rating or marking to make the AHJ happy.

Reply

Link copied. Please paste this link to share this article on your social media post.

ezgod87
Crewman ezgod87
Crewman

Posted: ‎2023-04-07 04:39 AM

0 Likes
0
2330
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-07 04:39 AM

For a school project I'm asked to design a temperature sensor with transistors exclusively.

I need to use the characteristics of a temperature-dependent transistor and implement a transistor(s) amplifier which will fix the sensitivity of the sensor.

I can only use bipolar and FET transistors, resistors and a continuous power supply +/- 15V.

router login 192.168.l.l
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore