Hello
Anybody have SLEASLXXB on their desk to test if setpoint change is preserved after power outage?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-17 09:41 PM
Just happened to see this topic. I'm R&D for SLEA. After power cycle, the setpoint value will be reset to 18C.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-03 10:20 PM
@Ami_Saha I think you are the Offer Manager, can you assist with this question?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-17 09:41 PM
Just happened to see this topic. I'm R&D for SLEA. After power cycle, the setpoint value will be reset to 18C.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-07-18 03:01 AM
@Huiye_Dai thanks for testing this!
This means that power supply for SLEASLXXB must be protected against power loss because after building power outage setpoint will reset to 18 in entire building.
Eventually BMS/BAS controller must detect power outage and backup last setpoint until user interaction.
@Ami_Saha do you think it is possible to backup setpoint setting in existing hardware/udpate firmware for new products?