SHD100-T: Fluctuations in the Relative Humidity readings

Intelligent Devices Forum

Schneider Electric support forum about all Intelligent Field Devices brands of Sensors, Thermostats, Glass Touch Panels, Valves and Actuators

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Intelligent Devices
  • Intelligent Devices Forum
  • SHD100-T: Fluctuations in the Relative Humidity readings
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
CraigEl
Administrator CraigEl Administrator
42
MikaelKrantz
Guinan MikaelKrantz Guinan
11
Gary
Gary Schneider Alumni (Retired)
11
View All

Recommended Forums

  • SmartConnector Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Intelligent Devices Forum
Start a Topic
Solved
Makarand988
Crewman Makarand988
Crewman

Posted: ‎2022-12-13 05:39 AM

0 Likes
2
2458
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-13 05:39 AM

SHD100-T: Fluctuations in the Relative Humidity readings

Hi

I am using SHD100-T to measure Temperature & Relative Humidity in return air duct along with ASB-36.

I was frustrated because of too much fluctuations in relative humidity readings, where as Temperature reading was very stable.

error.jpeg

Initially I thought it is because of EM interference of AHU motor cables, hence I changed the sensor cable route (and used twisted pair, shielded cable). I did the wiring of the ASB-36 as per its installation sheet.

Also added threshold of 1% in input configuration. but there was no improvement. 

I also tried by replacing the sensor with new one, but it didn’t work.

I observed these fluctuations when I increse the Fan speed.

At last, I used the same sensor by removing its metal cap, and I didn’t expect it, but surprisingly the problem solved. And Now I am getting stable readings.

afteraftersensorsensor

Now I am curious to know the purpose of this brass metal cap, is it just meant for the protection of sensing element ?

Are the flucutions in the RH readings is the because of turbulent air flow in the return air duct ?

Will it give wrong readings if I used the sensor without cap ?

What is the correct location to mount the duct sensor (sidewall or top) ?

 

Labels
  • Labels:
  • Temperature Humidity & Air quality Sensors
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Ted_Roman
Picard Ted_Roman Picard
Picard

Posted: ‎2022-12-20 05:34 PM

0 Likes
0
2407
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-20 05:34 PM

@Makarand988 

I am not familiar with this specific device but my guess is your fluctuations may be due to ground reference. Check out this web help topic. 

https://ecostruxure-building-help.se.com/bms/topics/show.castle?id=11941&locale=en-US&productversion... 

A few comments:

  • disassembly of field devices is generally not recommended unless following manufacturers documentation for repair
  • Mounting on side or top of ductwork is is usually acceptable for most devices but I prefer sidewall in middle of airstream. While mounting on bottom can lead to condensation entering device and damaging it.
  • I believe the brass cap is a part of the sensor and required for proper operation probably to diffuse air as it enters the sensing element . The datasheet calls it a filter assembly.

Best of luck,

Ted

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

ThomasSiefert
Spock ThomasSiefert Spock
Spock

Posted: ‎2023-02-06 03:52 PM

0 Likes
0
2245
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-02-06 03:52 PM

Hmmm, it would be interesting so see what would happen if you connected the tip to ground.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Ted_Roman
Picard Ted_Roman Picard
Picard

Posted: ‎2022-12-20 05:34 PM

0 Likes
0
2408
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-20 05:34 PM

@Makarand988 

I am not familiar with this specific device but my guess is your fluctuations may be due to ground reference. Check out this web help topic. 

https://ecostruxure-building-help.se.com/bms/topics/show.castle?id=11941&locale=en-US&productversion... 

A few comments:

  • disassembly of field devices is generally not recommended unless following manufacturers documentation for repair
  • Mounting on side or top of ductwork is is usually acceptable for most devices but I prefer sidewall in middle of airstream. While mounting on bottom can lead to condensation entering device and damaging it.
  • I believe the brass cap is a part of the sensor and required for proper operation probably to diffuse air as it enters the sensing element . The datasheet calls it a filter assembly.

Best of luck,

Ted

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

ThomasSiefert
Spock ThomasSiefert Spock
Spock

Posted: ‎2023-02-06 03:52 PM

0 Likes
0
2246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-02-06 03:52 PM

Hmmm, it would be interesting so see what would happen if you connected the tip to ground.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore