Intelligent Devices Forum
Schneider Electric support forum about all Intelligent Field Devices brands of Sensors, Thermostats, Glass Touch Panels, Valves and Actuators
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-09-15 09:07 PM . Last Modified: 2021-03-17 03:53 AM
Hi,
I have 10 + MP130-24M Actuators installed on a project. All are giving ten volt feed back no mater what the signal is. The feed back only modulates (10 volts- 0 Volts-10 -Volts) When the reset button is pushed. All cables and signals have been proven. I thought it may have been a faulty one at first but each successive actuator has the same issue. MP500 and MP300 installed all work perfectly.
Any ideas on a fix would be greatly appreciated.
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-09-27 10:54 AM
the MP130 actuator with feedback is the MP130-24MP
P for position feedback.
You need to first ensure the actuator is mounted on the valve, powered and calibrated. Output X is not correct until the actuator is calibrated.
You may need to reset the actuator for it to re-calibrate, and this reset is recommended if the manual override is ever operated.
There is a small push button on the PCBA next to the Dip-switches that re-sets the actuator.
Specification sheet attached
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-09-26 07:21 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-09-26 07:21 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-09-27 10:54 AM
the MP130 actuator with feedback is the MP130-24MP
P for position feedback.
You need to first ensure the actuator is mounted on the valve, powered and calibrated. Output X is not correct until the actuator is calibrated.
You may need to reset the actuator for it to re-calibrate, and this reset is recommended if the manual override is ever operated.
There is a small push button on the PCBA next to the Dip-switches that re-sets the actuator.
Specification sheet attached
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2019-09-29 04:49 PM
Thanks for the feedback.
It looks like what the issue is, I was commissioning the plant before the chilled water was running. Once a pressure was in the pipes and a reset/power cycle was done on the actuator, the valves stroked and started giving the correct feedback.
I am a bit worried that with intermittent loss off chilled water pressure which happens often during the commissioning phases of construction, I may have to run around site and reset this model.
Link copied. Please paste this link to share this article on your social media post.