Is it possible to disable TC900 FAN/Ventilation?

Intelligent Devices Forum

Schneider Electric support forum about all Intelligent Field Devices brands of Sensors, Thermostats, Glass Touch Panels, Valves and Actuators

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Intelligent Devices
  • Intelligent Devices Forum
  • Is it possible to disable TC900 FAN/Ventilation?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
CraigEl
Administrator CraigEl Administrator
42
MikaelKrantz
Guinan MikaelKrantz Guinan
11
Gary
Gary Schneider Alumni (Retired)
11
View All

Recommended Forums

  • SmartConnector Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Related Products
product field
Schneider Electric
EcoStruxure™ Building Operation

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Intelligent Devices Forum
Start a Topic
Solved
ld94
Lieutenant JG ld94
Lieutenant JG

Posted: ‎2023-03-13 02:20 AM . Last Modified: ‎2023-03-13 02:24 AM

0 Likes
5
2757
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-13 02:20 AM . Last Modified: ‎2023-03-13 02:24 AM

Is it possible to disable TC900 FAN/Ventilation?

Good morning all,

my customer has the following request: when I have the start from an external thermostat the ventilation can be ON, otherwise it should be OFF (no low speed, completely off).
Is there a Modbus register that I can use to shut off the fan completely?

The only thing that came to my mind is to create an MTA that automatically matches the set point with the temperature read by the TC until the thermostat close the contact and set the register 16 "Fan operation after setting temperature is reached" to 0.

Any other solutions?

Thanks in advance,
LD

 

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
PatrickDumas
Captain PatrickDumas Captain
Captain

Posted: ‎2023-03-15 12:07 PM . Last Modified: ‎2023-03-15 12:13 PM

0 Likes
1
2705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-15 12:07 PM . Last Modified: ‎2023-03-15 12:13 PM

Hello,

I also think you have found the best and only option to ensure to turn the Fan Off (all speed) from a ModBus command.
- Setpoint = Room Temp
- Fan operation after setting temperature is reached = 0 (this may be left set to 0 depending on application)

- May also have to force Fan Mode = Auto (Register 5 = 03) ...conditional to Auto Fan = Enable.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
CraigEl
Administrator CraigEl Administrator
Administrator

Posted: ‎2023-03-14 05:28 PM

0 Likes
0
2722
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-14 05:28 PM

I'm not sure I 100% understand what is required but your idea does sound feasible.

Reply

Link copied. Please paste this link to share this article on your social media post.

Troy_Wecker
Lieutenant JG Troy_Wecker Lieutenant JG
Lieutenant JG

Posted: ‎2023-03-15 10:45 AM

0 Likes
0
2711
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-15 10:45 AM

I will contact the Offer Manager for this product to answer this question.   Please standby.

Reply

Link copied. Please paste this link to share this article on your social media post.

PatrickDumas
Captain PatrickDumas Captain
Captain

Posted: ‎2023-03-15 12:07 PM . Last Modified: ‎2023-03-15 12:13 PM

0 Likes
1
2706
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-15 12:07 PM . Last Modified: ‎2023-03-15 12:13 PM

Hello,

I also think you have found the best and only option to ensure to turn the Fan Off (all speed) from a ModBus command.
- Setpoint = Room Temp
- Fan operation after setting temperature is reached = 0 (this may be left set to 0 depending on application)

- May also have to force Fan Mode = Auto (Register 5 = 03) ...conditional to Auto Fan = Enable.

Reply

Link copied. Please paste this link to share this article on your social media post.

Troy_Wecker
Lieutenant JG Troy_Wecker Lieutenant JG
Lieutenant JG

Posted: ‎2023-03-16 09:44 AM

0 Likes
0
2686
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-16 09:44 AM

See Patrick Dumas reply

Reply

Link copied. Please paste this link to share this article on your social media post.

ld94
Lieutenant JG ld94
Lieutenant JG

Posted: ‎2023-03-23 12:06 AM

In response to PatrickDumas
0 Likes
0
2641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-23 12:06 AM

Thank you for the answer!
I'll try that.

Have a nice day.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore