How to measure the flow on PIBCV valve?

Intelligent Devices Forum

Schneider Electric support forum about all Intelligent Field Devices brands of Sensors, Thermostats, Glass Touch Panels, Valves and Actuators

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Building
  • Intelligent Devices
  • Intelligent Devices Forum
  • How to measure the flow on PIBCV valve?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
CraigEl
Administrator CraigEl Administrator
42
MikaelKrantz
Guinan MikaelKrantz Guinan
11
Gary
Gary Schneider Alumni (Retired)
11
View All

Recommended Forums

  • SmartConnector Forum

  • Metering & Power Quality

  • EcoStruxure IT Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Intelligent Devices Forum
Start a Topic
Solved
Diego_Ramirez
Ensign Diego_Ramirez
Ensign

Posted: ‎2021-05-18 01:38 AM

1 Like
5
8369
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-05-18 01:38 AM

How to measure the flow on PIBCV valve?

Hello all,

 

Could someone indicate me please how do I measure the flow on the PIBCV valves using the PT ports?

Labels
  • Labels:
  • Pressure Independent Valves and Actuators
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Simon_Firth
Lieutenant JG Simon_Firth Lieutenant JG
Lieutenant JG

Posted: ‎2021-05-25 10:25 AM

1 Like
0
8342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-05-25 10:25 AM

Hi, Measuring the flow is a relatively complex topic using the P-T ports and actually varies depending on which type (size/design) of valve we are using.

 

Document: F-28105 describes in detail the exact process for verifying the pressure and flow through all the DN10-250 valves.

F-27984 is the equivalent document for the 1/2" to 10" valves in the US with units of measurement in PSI and GPM

 

Basically, on the smaller valves, DN10 to DN32 (3/8" to 1-1/4") then the two P-T ports available are only used to verify the working pressure supplied to the valve is at the needed minimum level for the differential pressure regulator to work effectively.  If you do have the needed working pressure available, then you can be assured that the flow for any percentage setting scale on the valve is accurate and according to a document F-28130. This  F-28130 document declares the flow for any stroke limit (ie. flow setting considering the valve stroke limit is dependant on the set point setting).

 

For the larger valves with three test ports  where we are able to measure the full pressure drop across both the pressure regulator and the control valve portion of the valve as well as at the point in-between these components, then these pressures tapping's / readings are used alongside a table of effective Kvs to calculate the flow.. The comprehensive document guides: F-28105 Metric units / F-27984 - US units have these tables of effective Kvs/Cvs but there is also a simpler doc F-28088 available for just the DN40-250 valves.

 

 

Mr Valve

See Answer In Context

Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

greg_peterson_s
Crewman greg_peterson_s Crewman
Crewman

Posted: ‎2022-03-07 03:43 AM

In response to Ted_Roman
0 Likes
0
6867
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-07 03:43 AM

Please refer to SmartX PIBCV Pressure and Flow Verification F-27984 which you can be used with your commission/balancing agency. Here is the link.

 

https://ecoxpert.se.com/search?documentUUID=010b9c88-9c29-426b-a372-877c6fa54af2&title=PIBCV%20Smart...

 

Best Regards,

 

Greg Peterson

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Ted_Roman
Picard Ted_Roman Picard
Picard

Posted: ‎2021-05-25 08:37 AM

2 Likes
1
8347
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-05-25 08:37 AM

@Diego_Ramirez 

 

Should be able to use ports if required to verify flow the same as balancing valve. 

 

https://www.contractingbusiness.com/service/article/20870767/service-clinic-how-to-measure-flow-thro... 

 

Flow setpoint is set with dial on actuator.

 

Best regards,

Ted

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Simon_Firth
Lieutenant JG Simon_Firth Lieutenant JG
Lieutenant JG

Posted: ‎2021-05-25 10:25 AM

1 Like
0
8343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-05-25 10:25 AM

Hi, Measuring the flow is a relatively complex topic using the P-T ports and actually varies depending on which type (size/design) of valve we are using.

 

Document: F-28105 describes in detail the exact process for verifying the pressure and flow through all the DN10-250 valves.

F-27984 is the equivalent document for the 1/2" to 10" valves in the US with units of measurement in PSI and GPM

 

Basically, on the smaller valves, DN10 to DN32 (3/8" to 1-1/4") then the two P-T ports available are only used to verify the working pressure supplied to the valve is at the needed minimum level for the differential pressure regulator to work effectively.  If you do have the needed working pressure available, then you can be assured that the flow for any percentage setting scale on the valve is accurate and according to a document F-28130. This  F-28130 document declares the flow for any stroke limit (ie. flow setting considering the valve stroke limit is dependant on the set point setting).

 

For the larger valves with three test ports  where we are able to measure the full pressure drop across both the pressure regulator and the control valve portion of the valve as well as at the point in-between these components, then these pressures tapping's / readings are used alongside a table of effective Kvs to calculate the flow.. The comprehensive document guides: F-28105 Metric units / F-27984 - US units have these tables of effective Kvs/Cvs but there is also a simpler doc F-28088 available for just the DN40-250 valves.

 

 

Mr Valve
Attachments
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-16 02:27 AM . Last Modified: ‎2021-08-26 08:03 AM

0 Likes
0
7914
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-16 02:27 AM . Last Modified: ‎2021-08-26 08:03 AM

Mathematically it is easy to see how, as the authority of a control valve is defined as: N = DPv / (DPv + DPc). Where: DPv = Pressure drop across a fully open control valve DPc = Pressure drop across the remainder of the circuit.
 
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Alfred69
Ensign Alfred69
Ensign

Posted: ‎2022-03-06 11:23 PM . Last Modified: ‎2022-03-07 08:09 PM

0 Likes
0
6878
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-06 11:23 PM . Last Modified: ‎2022-03-07 08:09 PM


@mcdvoice survey wrote: 

Hello all,

 

Could someone indicate me please how do I measure the flow on the PIBCV valves using the PT ports?


The smaller valves, DN10 to DN32 (3/8" to 1-1/4") then the two P-T ports available are only used to verify the working pressure supplied to the valve is at the needed minimum level for the differential pressure regulator to work effectively. If you do have the needed working pressure available, then you can be assured that the flow for any percentage setting scale on the valve is accurate and according to a document F-28130.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

greg_peterson_s
Crewman greg_peterson_s Crewman
Crewman

Posted: ‎2022-03-07 03:43 AM

In response to Ted_Roman
0 Likes
0
6868
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-03-07 03:43 AM

Please refer to SmartX PIBCV Pressure and Flow Verification F-27984 which you can be used with your commission/balancing agency. Here is the link.

 

https://ecoxpert.se.com/search?documentUUID=010b9c88-9c29-426b-a372-877c6fa54af2&title=PIBCV%20Smart...

 

Best Regards,

 

Greg Peterson

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore