Posted: 2023-01-31 03:33 AM
Hello
Mounting instruction of EPD302 predicts mounting on straight air duct. How it works with curved ducts? How long after bending I can mount EPD302? Directly after bending or 5 duct diameters after bending?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-31 08:33 AM
@PiotrJakubczyk
I do not see this information in our documentation.
I did find some some information that may provide a good guide on the Veris website for the SE AA18, AA19, AA20
Provide smooth, straight duct sections a minimum of 8-1/2 diameters in length upstream and 1-1/2 diameters
downstream from the pitot tube.
Regards
Gary
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-31 08:33 AM
@PiotrJakubczyk
I do not see this information in our documentation.
I did find some some information that may provide a good guide on the Veris website for the SE AA18, AA19, AA20
Provide smooth, straight duct sections a minimum of 8-1/2 diameters in length upstream and 1-1/2 diameters
downstream from the pitot tube.
Regards
Gary