Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-11-03 12:22 AM
Hi,
I am using Zelio PLC SR3B101BD with SR3MBU01BD Modbus card and i am trying to read %MW16-19 registers. I can read %MW20-48 registers but when i read %MW16-19 I get zeros.
What's the problem?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-11-09 01:50 AM
Hi, The IOs of Zelio Logic are starting on Mobdus Register MW20 (decimal).
These values are always mapped to modbus.
If you want to read values from MW16-19 you need to write values into these Variabels.
If you don´t connect a value to these outputs. The modbus Value should alltimes 0.
I hope this will help you.