Hello!
I hav a setup with m221 in one building and into other building i installed tm3bceip with 3 tm3 modules. I configured it via configurator and pushed configuration in. Everything worked. It just stopped working and it is not communicating anymore. NS and IO lights are blinking. Status is configured and outputs are maintained to zero. In monitoring section i can see that output module wants to always reconcile. Is that the issue? Tried to swap it with other module also, still nothing.
ip configurations are all done correctly. What can i check further?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-10-21 12:36 AM
Okay, after digging in log, i discovered that Config via M2xxx is not allowed when 'TM3 Modules configuration via modbus commands' feature is enabled. Funny thing is that Schneider support didnt figure it out also. Simple mistake but wasted alot of my time. Hope this helps somone else.