Dear Sir / Madam,
Could you help with how to time sync the Harmony HMI (Vijeo) with the M262 PLC? Currently the M262 PLC is time syncing from an NTP source, however we cannot find any function / setting on the Vijeo project where you can enable / select the time sync source (NTP/PLC /other). Usually this opeion is under the Startup selection in the target however for our project this option is not available? Also the need to be time zone and DST adjusted.
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-04-02 07:52 AM
Hello,
I have the exact same issue with a M262 and HMIG3U, the thing is that I looked at the web service for the PLC and found a Date/Time menu.
From there, you have the possibility to change the TimeZone/DST.
And I wonder if it was the same thing for the HMI, because I can't access the web service yet.
Best Regards,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-04-08 07:07 AM
Hi
The GTU series don't support Time Management and Machine Expert driver doesn't support dialog table either.
So to use dialog table, you have to add one Modbus TCP driver in Vijeo:
Please find the attached Sample Machine Expert project.
This project is based on the sample project shown below and you can switch to M262 you are using
Greetings