Posted: 2025-08-22 06:44 AM
I need to equip the LUB32 with LUCB32FU and both fault contacts NO 97-98 and NC 95-96. Is this possible?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-08-27 12:06 AM
Hi PantheraInAutomation,
As these contacts exist on separate modules, you cannot use them together on the same starter.
You can use function module LUFDH11 which will provide you with a normally open and normally closed thermal overload fault contacts. Please not this module will require a separate voltage supply.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-08-27 11:50 PM
Hello Mr. DuMalt,
Thank you for your tip... that will do the trick.
Sincerely yours,
PantheraIA