TM172 ThreePointActuator control

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • TM172 ThreePointActuator control
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
32
LeTomas
Lt. Commander LeTomas Lt. Commander
11
RoozeeR
Lt. Commander RoozeeR Lt. Commander
6
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
6
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Industry Automation and Control Forum
lionginas_elekt
Ensign lionginas_elekt
Ensign

Posted: ‎2024-01-11 12:42 AM

0 Likes
5
1097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-11 12:42 AM

TM172 ThreePointActuator control

Hello.

In a HVAC project I use 3 point actuator control with PID and ThreePointActuator blocks.

ThreePointActuator block takes from PID difference of PV_current_value and PV_set_point and

generate Close or Open pulses. I wander why those pulses are very short by lenght. It results

that PID saturated to 100 % but the valve is open too little. I inserted TON timers to extend close

and open pulses, but I am not sure is it right way to use.

Appreciate any comments,

Best regards.

Attachments
Labels
  • Labels:
  • Smart Operations
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2024-01-11 01:00 PM

0 Likes
1
980
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-11 01:00 PM

Hi,

Normally you could directly connect the Digital Outputs for the actuator directly on the block. If the time puls is to short, then the value of uiMaxRuntime could be the problem. The Resolution of this value is 0.1s and not 1s. If you have a actuator which has a travel time from open to close with 90s you need to enter the value 900.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

lionginas_elekt
Ensign lionginas_elekt
Ensign

Posted: ‎2024-01-15 01:12 AM

In response to Bastian_Schmitz
0 Likes
0
956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-15 01:12 AM

Thanks for reply. uiMaxRuntime is correct. To figure out where is problem I did simulation with PID and ThreePointActuator. The first I did XCalibration = true, xClose go TRUE for 30 seconds (uiMaxRuntime = 300).

Then I set rPV and rSetp difference and wait for uiControlSignal for saturation to 1000. xOpen generated series of shot pulses. I am right if at this point I go to xManualMode = 1 (rManualValue = 0) xClose need to be

go TRUE the same time 30 s. But I see there only 5-6 sec. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2024-01-16 01:14 AM

0 Likes
0
932
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-16 01:14 AM

Did you use the AFB in a Timed or in a Background Task? I did not double check it, but I expect that the block should be run in a timed task. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2024-01-18 02:08 PM

0 Likes
1
924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-18 02:08 PM

The input uiControlSignal expect a value between 0...10000 (0,01%). That is a little bit strange because the PID gives as output 0....1000. I think that is the main case of your problem. I need also several time to read correctly this point in the documentation ?!?

Bastian_Schmitz_0-1705615682312.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

lionginas_elekt
Ensign lionginas_elekt
Ensign

Posted: ‎2024-01-19 05:04 AM

In response to Bastian_Schmitz
0 Likes
0
911
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-01-19 05:04 AM

In my case they are equal. The first one is PID output ranged 0...1000 and scaled 0.1% and the

second one is ThreePointActuator input ranged 0.....10000 and scaled 0.01%. Do you think it is problem.

 

lionginas_elekt_0-1705668957329.jpeg

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of