@TM172 Modbus TCP/IP Communication
Select a Country
  • Industrial Automation
  • @TM172 Modbus TCP/IP Communication
Bastian_Schmitz
Bastian_Schmitz Champion
38
LeTomas
LeTomas Mentor
14
ismailozinan
ismailozinan Leader
8
fuatdag
fuatdag
Explorer
Posted: ‎2024-06-03 06:51 AM
1744
Hi dear friends,
I need some help about communicate two TM172PDG42RI device's via modbus TCP/IP communication. I want to read value from TM172 to an other TM172 PLC. is it possible? if answer is yes can u explaine how it is possbile. Do u have any document with detailed explanation or any example project. Thanks for your answer.
In my project ı can read modbus value via Modbus Tool but i can't read via TM172 PLC.
  • Energy Efficiency
  • Process Automation Talks
  • Smart Design & Engineering
  • Training
Bastian_Schmitz
Champion
Posted: ‎2024-06-05 11:05 PM
A communication via Modbus TCP between two TM172 is possible via Configuration. You need only to create on one or booth controller the Modbus TCP Master function. Then you could configer your communication (via generic Modbus Object and FC3/16). An other possibility is via Programming and backgroundtask via the included Targetfunctions
StevenCho
StevenCho
Contributor
Posted: ‎2024-06-06 03:10 AM
Hi Fautdag,
Please take a look the attached sample program and variable list.
This is the example of MODBUS TCP configuration between two TM172.
(The program is built on ESME-HVAC V1.6.0)
statusVariableList.xlsx
TCP_Sample(Fautdag).zip