Posted: 2024-06-03 06:51 AM
@TM172 Modbus TCP/IP Communication
Hi dear friends,
I need some help about communicate two TM172PDG42RI device's via modbus TCP/IP communication. I want to read value from TM172 to an other TM172 PLC. is it possible? if answer is yes can u explaine how it is possbile. Do u have any document with detailed explanation or any example project. Thanks for your answer.
In my project ı can read modbus value via Modbus Tool but i can't read via TM172 PLC.
- Tags:
- english
Authentication Failed.
- Authentication Ticket Mismatched, failed authentication.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-05 11:05 PM
A communication via Modbus TCP between two TM172 is possible via Configuration. You need only to create on one or booth controller the Modbus TCP Master function. Then you could configer your communication (via generic Modbus Object and FC3/16). An other possibility is via Programming and backgroundtask via the included Targetfunctions
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-06-06 03:10 AM
Hi Fautdag,
Please take a look the attached sample program and variable list.
This is the example of MODBUS TCP configuration between two TM172.
(The program is built on ESME-HVAC V1.6.0)