Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.
Search in
Posted: 2021-10-12 11:14 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-10-12 11:14 PM
I am trying to read Total Harmonic Distortion from Energy Meter EM6400NG into PLC TM241CE40T using Modbus RTU on RS485 serial line. I am able to read all the holding registers that I need to read for my application from the energy meter into my PLC, except the modbus addresses above 10,000 range (Total Harmonic Distortion parameters addresses = 21300 onwards).
I am able to read the addresses from 21300 onwards in ModScan software but the same addresses do not work in PLC Modbus IOScanner (other addresses below 10,000 address location are easily being read). If I set the address offset for Modbus IOScanner as 21299 inside PLC software (SoMachine v4.3), then the value being read is '0'
Kindly help!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.