Operator Terminal Expert : Index 0 DropDown List

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • Operator Terminal Expert : Index 0 DropDown List
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
35
LeTomas
Lt. Commander LeTomas Lt. Commander
14
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
7
View All

Recommended Forums

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Related Products
product field
Schneider Electric
EcoStruxure™ Operator Terminal Expert 3.1

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Industry Automation and Control Forum
Start a Topic
rfond
Ensign rfond
Ensign

Posted: ‎2025-02-26 03:09 AM

0 Likes
10
2038
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-26 03:09 AM

Operator Terminal Expert : Index 0 DropDown List

Hello everyone,

I have another issue with EOTE. I have a selectable dropdown list, and I want to use index 0 from this list (my selection options are 0 = Stop / 1 = Auto / 2 = Manual). The problem is that the index always starts at 1. This is a big issue for me.

How can I use index 0?

Thanks!

Labels
  • Labels:
  • Process Automation Talks
  • Tags:
  • english
  • eote
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 10
Hennie_Smith
Lieutenant Hennie_Smith Lieutenant
Lieutenant

Posted: ‎2025-02-26 09:32 PM . Last Modified: ‎2025-02-26 09:33 PM

1 Like
0
2033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-26 09:32 PM . Last Modified: ‎2025-02-26 09:33 PM

Hi unfortunately there is no way the dropdown object to start with index 0. If this is on a faceplate (popup) you can probably add an additional 'Accept/Ok' button to write the (selected index - 1) to the PLC variable. Convertors will also not work as it can only convert direction PLC -> HMI and not the other way around.

Reply

Link copied. Please paste this link to share this article on your social media post.

rfond
Ensign rfond
Ensign

Posted: ‎2025-02-27 01:45 AM

0 Likes
0
2007
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-27 01:45 AM

Are any fixes planned for this version?
Is there a roadmap for EOTE's future development?

Reply

Link copied. Please paste this link to share this article on your social media post.

Hennie_Smith
Lieutenant Hennie_Smith Lieutenant
Lieutenant

Posted: ‎2025-03-16 10:38 PM

0 Likes
1
1950
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-16 10:38 PM

EOTE is the software that will be used going forward on all new HMI models. It is active product and regular updates are released.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

rfond
Ensign rfond
Ensign

Posted: ‎2025-03-18 12:25 AM

In response to Hennie_Smith
0 Likes
0
1937
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-18 12:25 AM

So can a fix be implemented for this issue?

Reply

Link copied. Please paste this link to share this article on your social media post.

ismailozinan
Commander ismailozinan Commander
Commander

Posted: ‎2025-03-18 09:51 AM . Last Modified: ‎2025-08-01 11:35 PM

1 Like
4
1926
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-18 09:51 AM . Last Modified: ‎2025-08-01 11:35 PM

Hi,

You can use convertor function with variable of item. I shared document at attached and shared  sample program that it made different method. You can reach to sample program via this link. 

 

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

rfond
Ensign rfond
Ensign

Posted: ‎2025-03-19 12:03 AM

In response to ismailozinan
1 Like
3
1902
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-03-19 12:03 AM

But the variable's direction is "One Way" :(.

I've already tried this solution, but it doesn't work.

Reply

Link copied. Please paste this link to share this article on your social media post.

Quintilian_Huynh
Quintilian_Huynh
Cadet

Posted: ‎2025-07-31 09:34 AM

0 Likes
0
1214
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-31 09:34 AM

 

 

I’m currently working with Schneider’s Operator Terminal Expert (EOTE) as well, and although my reply is a bit delayed, I recently ran into the same issue.

 

My goal was to assign a value from 0 to 3 to a DINT variable in the PLC based on the selection from a dropdown list.

I initially tried using a converter, but binding the variable to the object didn’t work: it seemed to expect a Boolean.

What ended up working for me was writing an onClick script for the dropdown component that subtracts 1 from the selected index and assigns it to the variable.

 

Here’s an example:

 

onClick($GraphicObject.ModeDropDown, () => {
    LS_PmpGrp001_W.Mode.Value = ($GraphicObject.ModeDropDown.SelectedIndex -1);
});
Hope this helps someone else running into the same challenge.
Reply

Link copied. Please paste this link to share this article on your social media post.

ismailozinan
Commander ismailozinan Commander
Commander

Posted: ‎2025-08-01 11:39 PM . Last Modified: ‎2025-08-01 11:53 PM

In response to rfond
1 Like
2
1183
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-08-01 11:39 PM . Last Modified: ‎2025-08-01 11:53 PM

I added sample program it works with two way Link 

Reply

Link copied. Please paste this link to share this article on your social media post.

Kris8888
Kris8888
Cadet

Posted: ‎2025-09-02 03:42 AM

In response to ismailozinan
0 Likes
1
983
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-02 03:42 AM

@ismailozinan What version of EOTE was this made in?

Reply

Link copied. Please paste this link to share this article on your social media post.

ismailozinan
Commander ismailozinan Commander
Commander

Posted: ‎2025-09-02 10:13 PM

In response to Kris8888
0 Likes
0
945
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-09-02 10:13 PM

@Kris8888 it made by EOTE 3.5 service pack-1. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore