Hi everyone,
I am Using Movicon next as a SCADA Software. My site located in a remote area. I need to connect OFS with Movicon Next via OPC UA. To do that What are the things needed to be installed on the site and which are the Ports to be Forwarded at the site firewall?
Regards
kpr
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-03-03 05:28 AM
you need to install at site:
OFS with driver you need.
and OPC UA option checked.
port for firewall 48400
there is also FAQ for this question.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-03-06 12:58 AM
Thank you for your response,
I'm going to connect OFS OPC with Movicon next(SCADA Software). Whether You tried with movicon or any other third party SCADA Software?.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-03-17 05:52 AM
Hi, while trying to connect ofs opc with Movicon next , i'm getting bad certificate Host Name Invalid error. How can rectify this issue?.
Regards,
Praveenraj.k
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-04-16 08:24 PM
Likely a bit late to the party on this, but might help someone in the future.
You likely don't have an appropriate SSL certificate assigned to the server.
You should have one with an appropriate subject alternative name associated. This will largely depend on how you end up referencing the server. Some common mistakes:
Essentially the SAN (Subject Alt Name) should include potential addresses used to reference the service internally.
Link copied. Please paste this link to share this article on your social media post.