Modbus Communication isses with ABB VSD
  • Industrial Automation
  • Modbus Communication isses with ABB VSD
Bastian_Schmitz
35
LeTomas
14
JerryBartlemay
7
ajith_iqsystems
Ensign ajith_iqsystems
Ensign
Posted: ‎2019-05-08 12:32 AM
3604
01.03 no of ABB VSD is connected to the AS-P via Modbus-RTU as slave Devices.
02.These VSDs are going to control via BMS.
03.The Control Point Configuration has attached here.
Requirement
In first startup, the VSD does not operate according to the BMS Command. But after one more start & stop command, it started to operate properly via BMS. It occurs mainly after an power failure. But ABB VSD Vendor exhibited this function  using ModBusPoll software. First he commanded to the VSD & shutdown Power of VSD. After powerup the VSD again, it was operated with the command. But this was not happend in Struxureware.
Please give me a solution as soon as possible.
As my observation, this VSD vendor, initially configured Modbus operating point(Register) as a reable & writable point. But it did not worked. Then he configured that point as only writable point & it operated properly
Replies 4
Omaelk
Janeway Omaelk
Janeway
Posted: ‎2019-05-08 04:49 AM
3
3598
Hello @Jean_Commeignes , I think you can help @ajith_iqsystems for the issue above
ajith_iqsystems
Ensign
Posted: ‎2019-05-09 08:46 AM
In response to Omaelk
3584
Please give me a solution for this issue as soon as possible
Jean_Commeignes
Administrator Jean_Commeignes Administrator
Posted: ‎2019-05-15 07:15 AM
In response to ajith_iqsystems
3569
Hello Ajith,
Would be more than happy to help.
I seem understanding that your Modbus communication issues with ABB VSD, are in the scope of Building Management Systems, for HVAC control aplications (and not Industrial Automation Systems).
If I am right, could you please tell me what is or what are Schneider Electric BMS controller or server ranges involved?
Best regards
Jean
Power & Building Exchange Community Manager
Jean COMMEIGNES
Schneider Electric Community Manager for Power & Building
Jean_Commeignes
Posted: ‎2019-05-15 07:22 AM
In response to Jean_Commeignes
Sorry Ajith,
Lately saw your previous post, explaining your issue, I could understand.
So,  will connect with you through private message, as this forum is Industrial Automation focused.
Jean
Power & Building Community Manager
Jean COMMEIGNES