Magelis XBTGT HMI with PLC M241
  • Industrial Automation
  • Magelis XBTGT HMI with PLC M241
Bastian_Schmitz
35
LeTomas
14
JerryBartlemay
7
EcoStruxure™ Machine Expert
Olofsson
Crewman Olofsson
Crewman
Posted: ‎2022-10-05 05:27 AM
2242
I have a project where I have new PLC M241 and an old Magelis XBTGT HMI (XBTGT 5330). The plan is to connect these two with modbusTCP but I have some difficulties to get this to work. I think mostly because the HMI model is deprecated. But for now, I need to work with what I have.
In Vijeo I have selected the modbusTCP driver and I have set my variables as external.
In Machine Expert I have the Generic Modbus TCP slave.
And as you can see, I have an alarm. Which is not so helpful 😕
The Industrial Ethernet Manager is happy though
Does anyone have an idea on where I have messed up? Or where I should continue with my trouble shooting?
Thanks!
  • Training
Svenmj
Ensign Svenmj Ensign
Ensign
Posted: ‎2022-10-05 06:33 AM
In response to Olofsson
2214
If you are using the Modbus Driver you define addresses in VJD, ie 40001 is %MW0 in PLC depending on your settings on the Driver
LeTomas
Lt. Commander
Posted: ‎2022-10-05 06:42 AM
Hi @Olofsson ,
Please take a look into this video to connect teh PLC with an HMI in Vijeo Designer using the Machine Expert protocol:
https://youtu.be/riQv-gvADM4
ANother solution using the MOdbusTcp driver in HMI take a look into the next application:
https://schneider-electric.box.com/s/cap8l6or3w901frwg3czaau42t1etgja
More information about the address in the PLC:
https://youtu.be/xsS_JNg-5MM
Good luck!
Replies 5
Svenmj
Ensign
Posted: ‎2022-10-05 06:02 AM
2232
Hi
You don't need to set in a Modbus Slave in the M241. The PLC should act as a Modbus Server and you have to activate the protocol under the Ethernet interface in Machine Expert
Olofsson
Crewman Olofsson
Crewman
Posted: ‎2022-10-05 06:22 AM
In response to Svenmj
2223
That takes care of my alarm alright 🙂
But then what? How do I find the addresses to the variables in the HMI?
Svenmj
Ensign
2215
LeTomas
Lt. Commander
Hi @Olofsson ,
Good luck!
Olofsson
Crewman Olofsson
Crewman
Posted: ‎2022-10-06 12:40 AM
So simple...
I got it to work with a slave but then I had to declare the inputs and outputs. This is far better!
Big thanks !