MEMORY ADDRESS OF DDT VARAIBLE CHANGES AUTOMATICALLY IN M580 CONTROL EXPERT.

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • MEMORY ADDRESS OF DDT VARAIBLE CHANGES AUTOMATICALLY IN M580 CONTROL EXPERT.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
32
LeTomas
Lt. Commander LeTomas Lt. Commander
12
RoozeeR
Lt. Commander RoozeeR Lt. Commander
6
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
6
View All
Related Products
product field
Schneider Electric
Modicon M580

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Industry Automation and Control Forum
Solved
kishore1march
Lieutenant JG kishore1march
Lieutenant JG

Posted: ‎2023-04-15 01:08 AM

0 Likes
3
1807
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-15 01:08 AM

MEMORY ADDRESS OF DDT VARAIBLE CHANGES AUTOMATICALLY IN M580 CONTROL EXPERT.

Dear,

 

I created a DDT and given a starting memory address, so the variables that are inside the DDT are auto assigned as per given starting address. 

 

Now i have  noticed many times the memory address inside the DDT changes automatically after download with any man intervention.

 

Can u help how to stop the autochanges of memory address.

 

Kindly see the attaches picture with redmarkup.

 

 

Labels
  • Labels:
  • Smart Operations
  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
kishore1march
Lieutenant JG kishore1march
Lieutenant JG

Posted: ‎2023-04-20 06:04 AM

1 Like
0
1745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-20 06:04 AM

@Mnabil @Bosswaffle 

Dears, 

Thanks for your time.

 

Issue was resolved.

My mistake was - real address were started with odd numbers(%mw7) which lead to wrong display of values. 

I corrected the address to even numbers(%mw6) which fixed this problem.

 

https://www.se.com/in/en/faqs/FA194559/

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Mnabil
Lieutenant JG Mnabil Lieutenant JG
Lieutenant JG

Posted: ‎2023-04-15 01:19 AM

0 Likes
0
1802
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-15 01:19 AM

Hello @kishore1march 

You can change the setting of DTM to be the same as the attached print screens and use the DDT structure to get the data and the status of the communication "Freshness"

 

Attachments
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Bosswaffle
Lt. Commander Bosswaffle
Lt. Commander

Posted: ‎2023-04-19 08:31 PM

0 Likes
0
1755
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-19 08:31 PM

The %MW address changes? or the internal adress %UW? How many instances of the DDT do you have? Can you attach a picture of the structure?

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

kishore1march
Lieutenant JG kishore1march
Lieutenant JG

Posted: ‎2023-04-20 06:04 AM

1 Like
0
1746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-04-20 06:04 AM

@Mnabil @Bosswaffle 

Dears, 

Thanks for your time.

 

Issue was resolved.

My mistake was - real address were started with odd numbers(%mw7) which lead to wrong display of values. 

I corrected the address to even numbers(%mw6) which fixed this problem.

 

https://www.se.com/in/en/faqs/FA194559/

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of