Dear,
I created a DDT and given a starting memory address, so the variables that are inside the DDT are auto assigned as per given starting address.
Now i have noticed many times the memory address inside the DDT changes automatically after download with any man intervention.
Can u help how to stop the autochanges of memory address.
Kindly see the attaches picture with redmarkup.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-20 06:04 AM
Dears,
Thanks for your time.
Issue was resolved.
My mistake was - real address were started with odd numbers(%mw7) which lead to wrong display of values.
I corrected the address to even numbers(%mw6) which fixed this problem.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-15 01:19 AM
Hello @kishore1march
You can change the setting of DTM to be the same as the attached print screens and use the DDT structure to get the data and the status of the communication "Freshness"
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-19 08:31 PM
The %MW address changes? or the internal adress %UW? How many instances of the DDT do you have? Can you attach a picture of the structure?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-04-20 06:04 AM
Dears,
Thanks for your time.
Issue was resolved.
My mistake was - real address were started with odd numbers(%mw7) which lead to wrong display of values.
I corrected the address to even numbers(%mw6) which fixed this problem.