M580 ENOC0311 READ_VAR function for reading OTB holding registers

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • M580 ENOC0311 READ_VAR function for reading OTB holding registers
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
32
LeTomas
Lt. Commander LeTomas Lt. Commander
12
RoozeeR
Lt. Commander RoozeeR Lt. Commander
6
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
6
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Control Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Industry Automation and Control Forum
PedroR
Ensign PedroR
Ensign

Posted: ‎2024-09-25 03:56 PM

0 Likes
6
1170
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-25 03:56 PM

M580 ENOC0311 READ_VAR function for reading OTB holding registers

Hello,

 

When trying to read data (Holding Registers) from an OTB (OTB1E0DM9LP) via ENOC 0311 card and using the READ_VAR function, I always encounter error 16#07 Problem in sending to the destination in the communication Management structure.

However, if the READ_VAR is sent to a Modbus Slave simulator, via the same ENOC 0311 port, pointing to the same OTB address (same Address syntax for the ADDMX function), the communication is successful. '0.2.0{IP Address}1'

The same success is obtained if READ_VAR is sent via the M580 CPU service port instead of the ENOC 0311 card. '0.0.3{IP Address}1'

 

Any idea of ​​what could cause this communication problem with the OTB when communicating via ENOC 0311?

 

Thank you in advance,

 

Pedro R.

Attachments
Labels
  • Labels:
  • Process Automation Talks
  • Tags:
  • english
  • ENOC0311
  • m580
  • otb
  • READ_VAR
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
MatthewM
Lt. Commander MatthewM
Lt. Commander

Posted: ‎2024-09-25 09:26 PM

1 Like
2
1139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-25 09:26 PM

Are you saying the CPU can read the OTB, but the NOC can't?  Or are you saying that both the CPU and NOC can read the simulator?

Try without the 1 on the end, as that is telling it to read Modbus node ID 1, which the OTB may not recognise.  Failing that try 255.  For example, when using a READ_VAR on a ETG100 ModbusTCP to Modbus 485 Gateway, the response #07 is reported by the ETG100 not being able to contact slave 1 on its serial side.  Some devices care about the slave ID, others don't.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Ricard
Lieutenant Ricard Lieutenant
Lieutenant

Posted: ‎2024-09-26 01:08 AM

0 Likes
2
1115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-26 01:08 AM

Hello Pedro,

I would do the same, remove of ID node of the ADDMX, on the other hand I would recommend you that use the IOScanning with a Genereric Modbus DTM, it's more easy to configure and forget all the management of this comunication.

 

If you can't resolve it, create a case in technical support Portugal and we will see in more deeply it

 

Best Regard

Ricard

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

PedroR
Ensign PedroR
Ensign

Posted: ‎2024-09-26 03:47 AM

In response to MatthewM
0 Likes
1
1105
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-26 03:47 AM

Hello MatthewM,

 

M580 can read the OTB or the Modbus Simulator.

ENOC 0311 can only read the Modbus Simulator, not the OTB.

 

I've tried with ID 1 and without at the end of address sintax. In CPU works with both, with ENOC 0311 it doesn't work.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

PedroR
Ensign PedroR
Ensign

Posted: ‎2024-09-26 03:52 AM

In response to Ricard
1 Like
1
1105
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-26 03:52 AM

Hello Ricard,

 

I've tried with ID 1 and without at the end of address sintax. In CPU works with both, with ENOC 0311 it doesn't work.

 

I can't use IO Scanning, i can't stop PLC every time i need to add a new communication. 

I need to use READ_VAR func.

 

I have already created a case in Schneider PT Support.

 

Thank you.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

MatthewM
Lt. Commander MatthewM
Lt. Commander

Posted: ‎2024-09-26 08:57 PM

In response to PedroR
0 Likes
0
1079
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-09-26 08:57 PM

I just noticed that you mention ADDMX.  Have you tried ADDM?  I am looking at what we have done for PLC (M340 and M580) PtoP comms and they all use ADDM, not ADDMX.  I am not sure what the difference is between the two functions.  Also, we have only used the eNOC 0301, not the eNOC 0311, so there may be differences in behaviour from what I am expecting.

 

Can you enable 'port mirroring' on a port, and plug in laptop with Wireshark to inspect the Modbus packets for the working CPU vs not working eNOC?  I use Wireshark all the time for weird stuff like this.  It may provide evidence to help diagnose.  I also make extensive use of 'Modbus Tester' from laptop to interrogate the device, using Wireshark to monitor the exchange.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Ricard
Lieutenant Ricard Lieutenant
Lieutenant

Posted: ‎2024-10-07 11:28 PM

In response to PedroR
0 Likes
0
986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-10-07 11:28 PM

see you 😉

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of