M171 can't write value as Modbus Master

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • M171 can't write value as Modbus Master
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
32
LeTomas
Lt. Commander LeTomas Lt. Commander
11
RoozeeR
Lt. Commander RoozeeR Lt. Commander
6
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
6
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Industry Automation and Control Forum
Solved
summersiu
Lieutenant | EcoXpert Master summersiu Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2021-03-24 01:42 AM . Last Modified: ‎2021-03-24 07:33 PM

0 Likes
3
2351
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-24 01:42 AM . Last Modified: ‎2021-03-24 07:33 PM

M171 can't write value as Modbus Master

I am connecting my M171PBM27R (Act as Master) and my PC act as Slave to transfer value.

However, after I created function 06 and assigned "test1" into it, I still cannot change the value in Watch View.

(For example, I want to change 4 to 5 into Watchview and I can observe the change in Modbus Slave

The value will be auto change back. How can I change the value in Machine Expert?

 

Problem solved😁

 

Master_Write.png

 

 

Labels
  • Labels:
  • Smart Design & Engineering
  • Tags:
  • english
  • SoMachince HVAC
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Dave_Shore
Dave_Shore Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-03-24 02:47 AM . Last Modified: ‎2022-10-19 01:49 AM

In response to summersiu
0 Likes
0
2343
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-24 02:47 AM . Last Modified: ‎2022-10-19 01:49 AM

@summersiu 

I am not familiar with the Machine Expert product, but I found 

https://community.se.com/t5/b-ecostruxure-geo-scada-expert-forum/EcoStruxure%2525E2%252584%2525A2+Ma...

 

Home/Communities/SCADA & Telemetry Solutions/Geo SCADA Expert Forum/EcoStruxure(TM) Machine Expert - HVAC

 

I have often used Modbus Slave, ModPoll, ModScan etc and all work with EBO.

You could test Machine Expert using EBO (the AS is easily configured to work with Modbus RTU/RS485), but ModSlave should also work fine and may be better for simple testing.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
Dave_Shore
Dave_Shore Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-03-24 02:05 AM

0 Likes
2
2348
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-24 02:05 AM

Hi @summersiu 

Your question does not seem to involve EBO (this forum), It seems to be Machine Expert (M171?) to Modbus Slave

Is there a forum for the product you are using?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

summersiu
Lieutenant | EcoXpert Master summersiu Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2021-03-24 02:28 AM

In response to Dave_Shore
0 Likes
1
2346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-24 02:28 AM

@Dave_Shore May I know where I can ask question for Schneider Machine Expert?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Dave_Shore
Dave_Shore Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2021-03-24 02:47 AM . Last Modified: ‎2022-10-19 01:49 AM

In response to summersiu
0 Likes
0
2344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-03-24 02:47 AM . Last Modified: ‎2022-10-19 01:49 AM

@summersiu 

I am not familiar with the Machine Expert product, but I found 

https://community.se.com/t5/b-ecostruxure-geo-scada-expert-forum/EcoStruxure%2525E2%252584%2525A2+Ma...

 

Home/Communities/SCADA & Telemetry Solutions/Geo SCADA Expert Forum/EcoStruxure(TM) Machine Expert - HVAC

 

I have often used Modbus Slave, ModPoll, ModScan etc and all work with EBO.

You could test Machine Expert using EBO (the AS is easily configured to work with Modbus RTU/RS485), but ModSlave should also work fine and may be better for simple testing.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of