How to read input coil status with BMX NOM0200 (RS485) by READ_VAR

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • How to read input coil status with BMX NOM0200 (RS485) by READ_VAR
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
35
LeTomas
Lt. Commander LeTomas Lt. Commander
14
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
7
View All

Recommended Forums

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Industry Automation and Control Forum
Start a Topic
Solved
Himanshusingh3
Crewman Himanshusingh3 Crewman
Crewman

Posted: ‎2021-07-13 01:19 AM

0 Likes
8
4092
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-13 01:19 AM

How to read input coil status with BMX NOM0200 (RS485) by READ_VAR

Hi,

 

         We are going to integrate third party equipment on Modbus RS485 through  BMX NOM0200 in M580 system, we are able to scan all Holding register, input register but how to read/scan input coil status by using READ_VAR function block????

Labels
  • Labels:
  • Smart Design & Engineering
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
RoozeeR
Lt. Commander RoozeeR Lt. Commander
Lt. Commander

Posted: ‎2021-07-13 01:49 AM

0 Likes
7
4086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-13 01:49 AM

Hello,

The READ_VAR function is able to Holding register (%MW), Input register (%IW) and Inputs (%I or 1xxxxx references) and Coils (%M or 0xxxxx references): See READ_VAR help in Control Expert, regarding the object type input on the READ_VAR function:

Type of objects to read for Modicon M340 and M580 CPU:
  • ’%M’: internal bits
  • ’%MW’: internal words
  • ’%I’: input bits
  • ’%IW’: input words
R.Roozee
Sr Solution Architect (SAE Master)

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
RoozeeR
Lt. Commander RoozeeR Lt. Commander
Lt. Commander

Posted: ‎2021-07-13 01:49 AM

0 Likes
7
4087
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-13 01:49 AM

Hello,

The READ_VAR function is able to Holding register (%MW), Input register (%IW) and Inputs (%I or 1xxxxx references) and Coils (%M or 0xxxxx references): See READ_VAR help in Control Expert, regarding the object type input on the READ_VAR function:

Type of objects to read for Modicon M340 and M580 CPU:
  • ’%M’: internal bits
  • ’%MW’: internal words
  • ’%I’: input bits
  • ’%IW’: input words
R.Roozee
Sr Solution Architect (SAE Master)
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Himanshusingh3
Crewman Himanshusingh3 Crewman
Crewman

Posted: ‎2021-07-13 02:40 AM

In response to RoozeeR
0 Likes
6
4077
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-13 02:40 AM

Thanks for input, @RoozeeR 

 

I have one more question how we can reset slave devices which gone in Request time out mode by auto as per preset time, because in application devices will not be online all the time only will be online when ever in duty mode.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

RoozeeR
Lt. Commander RoozeeR Lt. Commander
Lt. Commander

Posted: ‎2021-07-13 02:52 AM

In response to Himanshusingh3
0 Likes
5
4068
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-13 02:52 AM

Please explain what do you mean by "how we can reset slave devices which gone in Request time out mode by auto as per preset time":

- Do you need to reset the device itself, or reset the READ_VAR function becuase of the timeout?

 

 

 

R.Roozee
Sr Solution Architect (SAE Master)
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Himanshusingh3
Crewman Himanshusingh3 Crewman
Crewman

Posted: ‎2021-07-13 02:55 AM

In response to RoozeeR
0 Likes
4
4061
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-13 02:55 AM

@RoozeeR  not slave devices we want to reset READ_VAR FB which gone in Request time out

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

RoozeeR
Lt. Commander RoozeeR Lt. Commander
Lt. Commander

Posted: ‎2021-07-14 12:33 AM

In response to Himanshusingh3
0 Likes
3
4044
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-14 12:33 AM

You have to set the request timeout value in the Communication Management Parameter (Gest Input):

 
 

Annotation 2021-07-14 092328.png

Please note the value given is *100 mS (10 = 1 second). Make sure the timeout value is longer than the  reaction time of the device.

With Timeout, the Function will exit with request timeout and ready for a new command.

If you set the Timeout = 0, the timeout time is infinite, so the function will not exit: Do not use a 0 value.

If this happens you can use the CANCEL function to reset .

R.Roozee
Sr Solution Architect (SAE Master)
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Filipe_Brito
Crewman Filipe_Brito
Crewman

Posted: ‎2022-12-08 05:10 AM

In response to RoozeeR
0 Likes
2
3177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-12-08 05:10 AM

Good Morning;

if I have a very large timeout, can this be a problem? I have 65 blocks of read_var and a timeout = 1000 and I am not able to read all the blocks.

Reply

Link copied. Please paste this link to share this article on your social media post.

chrism1
chrism1
Cadet

Posted: ‎2024-02-08 07:58 AM

In response to Filipe_Brito
0 Likes
1
2486
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-08 07:58 AM

Did you ever fix your problem. I am currently reading 50 blocks of read_var and a timeout of 500 and i am not able to read all the blocks. Does increasing the timeout help?

Reply

Link copied. Please paste this link to share this article on your social media post.

MatthewM
Lt. Commander MatthewM
Lt. Commander

Posted: ‎2024-02-11 02:45 PM

In response to chrism1
0 Likes
0
2477
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-02-11 02:45 PM

I think this should be a new thread.  What do you mean by "50 blocks".  Do you mean you have 50 READ_VAR instances, or 1 READ_VAR with 1 read of 50 words, or 1 READ_VAR with 50 reads of x number of words?

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore