How to connect HMIST6400 to TM221CE24R PLC?
  • Industrial Automation
  • How to connect HMIST6400 to TM221CE24R PLC?
Bastian_Schmitz
35
LeTomas
14
JerryBartlemay
7
EcoStruxure™ Operator Terminal Expert 3.1
EcoStruxure™ Machine Expert - Basic
jhonut
Ensign jhonut
Ensign
Posted: ‎2021-02-25 05:05 AM
6054
I'd like to connect a HMIST6400 (programmed with ESOTE) with a TM221CE24R PLC (programmed with MachineExpert Basic).
I have exported the PLC symbols, but MEB allows only the .csv format which is not recognized by HMI.
How could I connect these two devices?
  • Smart Design & Engineering
  • Training
Bastian_Schmitz
Admiral
Posted: ‎2021-02-26 04:28 AM . Last Modified: ‎2021-02-26 04:33 AM
6039
The way is easier than you expect.
Add a SE Modbus TCP driver (or SIO)
And then import the Basic file via symbol import
Bastian_Schmitz
Admiral
6040
LeTomas
Lt. Commander
Posted: ‎2021-02-26 04:51 AM
Dear @jhonut ,
I have made the next video of how to connect the HMISTO7 to a M221.... is the same for the HMIST6****:
https://schneider-electric.box.com/s/av7nek0zbdltp6oh7qfuysfiimx2uomh
Best regards,
Letomas
jhonut
Ensign jhonut
Ensign
Posted: ‎2021-02-26 04:53 AM . Last Modified: ‎2021-02-26 05:04 AM
In response to Bastian_Schmitz
Thanks for your reply, @Bastian_Schmitz !
I have done as you suggested but I get an error: "Invalid device address. Enable or disable IEC address mode in the equipment." How should I do this? It's true that I don't use Modbus addresses but memory addresses.
Later edit. I have seen the video suggested by @LeTomas and I've how he's done it.