Establish ethernet connection between HMIST6500 and M251

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • Establish ethernet connection between HMIST6500 and M251
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
35
LeTomas
Lt. Commander LeTomas Lt. Commander
14
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
7
View All

Recommended Forums

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Related Products
product field
Schneider Electric
EcoStruxure™ Operator Terminal Expert 3.1
product field
Schneider Electric
Harmony HMI
product field
Schneider Electric
EcoStruxure™ Machine Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Industry Automation and Control Forum
Start a Topic
Solved
jhonut
Ensign jhonut
Ensign

Posted: ‎2021-02-02 01:35 AM

0 Likes
5
8357
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-02 01:35 AM

Establish ethernet connection between HMIST6500 and M251

Hello,

 

I'd like to communicate between HMIST6500 panel and TM251MESE PLC. As driver, in EcoStruxureOperator Terminal, I've chosen Schneider Electric-SoMachineNetwork where I set the PLC IP address (192.168.44.10).

HMI_Driver.PNG

 

In Machine Expert Logic Builder I'm using Generic_EtherNet_IP_device (I'm not sure is the right one). I've set panel's IP address (192.168.44.2) but a red triangle is shown. 

ethernet2.PNG

EthernetIp_device.PNG

 

What am I missing? Are there any other settings I should make in order to be able to have communication between devices?

Another question would be how to address a variable in ESOT through ethernet? For example, if I want to set, from HMI, a value for %MW20, how it should be addressed?

Labels
  • Labels:
  • Connected Products
  • Smart Design & Engineering
  • Training
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
LeTomas
Lt. Commander LeTomas Lt. Commander
Lt. Commander

Posted: ‎2021-02-02 02:11 AM

2 Likes
4
8345
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-02 02:11 AM

Hi @jhonut ,

 

I have made this video of how to connect the M2xx with an HMI in EOTE (EcoStruxure Operator Terminal Expert):

 

https://schneider-electric.box.com/s/j5liqwbdk3yf6jcmeyp55o3unfqgnf8e

 

I believe this is going to help you.

 

Best regards,

 

Leandro

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
LeTomas
Lt. Commander LeTomas Lt. Commander
Lt. Commander

Posted: ‎2021-02-02 02:11 AM

2 Likes
4
8346
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-02 02:11 AM

Hi @jhonut ,

 

I have made this video of how to connect the M2xx with an HMI in EOTE (EcoStruxure Operator Terminal Expert):

 

https://schneider-electric.box.com/s/j5liqwbdk3yf6jcmeyp55o3unfqgnf8e

 

I believe this is going to help you.

 

Best regards,

 

Leandro

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

jhonut
Ensign jhonut
Ensign

Posted: ‎2021-02-02 04:24 AM

In response to LeTomas
0 Likes
0
8334
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-02-02 04:24 AM

@LeTomas , many thanks for your reply! Though I have one question. How can I have access to https://schneider-electric.app.box.com/ ? I think this kind of videos should be accessed by everyone who's using Schneider software tools. Once again, thank you for your time and solution!

 

Have a great day!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-08-04 03:33 AM

In response to LeTomas
0 Likes
2
7823
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-04 03:33 AM

Hi Leandro,

 

I am also struggling to get the HMIST6600 to communicate with a TM251MESE. I followed your video which was great regarding tags, however I can only see that you configured the HMI to talk to the PLC via serial. Can you please give an explanation as to how to configure the communication via Ethernet?

 

Thanks, Ben

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

LeTomas
Lt. Commander LeTomas Lt. Commander
Lt. Commander

Posted: ‎2021-08-05 12:22 AM

In response to Anonymous user
0 Likes
1
7815
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-08-05 12:22 AM

Hi @Anonymous user ,

 

I have checked the video ( https://youtu.be/ZGvNAPbo-Hs ) and the connection was using the ethernet port of the devices.

 

What you need to do is:

 

On the PLC:

1) Set the ip address and nodename.

2) Add the symbol configuration.

3) Select the variables that you want to share with the HMI.

4) Generate the XML file.

5) Download the app to the HMI ( check if you are going to use the security)

 

On the HMI:

1) Set the ip address of the HMI (same network as the PLC)

2) Add the SoMachine/Machine Expert driver

3) Configure the driver as nodename (use the nodename of the PLC).

4) Check the security on the PLC to match the configuration on the HMI.

5) Import the variable the from the XML file.

6) Download the application to the HMI

 

I believe these are the steps to follow, sorry if miss something in the middle. The video has the complete explanation.

 

Best regards,

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

SESA528
Commander SESA528 Commander
Commander

Posted: ‎2022-02-08 08:55 AM

In response to LeTomas
0 Likes
0
7214
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-02-08 08:55 AM

HI Team,

 

I have a  trouble with HIM when I power-on HMI, i accepted but HMI not operation. Pls help me. Thanks very much

IMG_1613 (1).jpg

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon