Hello everyone,
I'm currently working on a project that adjusts the speed of a water pump based on the outlet pressure. I plan to use a PID controller for this purpose. However, I couldn't find any auto-tuning functionality within the project libraries. Manually tuning the PID parameters on-site would be quite time-consuming, so I'm looking for a way to implement auto-tuning using the PLC. Has anyone tackled something similar or have suggestions on how to approach this?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-04 11:09 PM
Have you seen the FAQ here?
https://www.se.com/in/en/faqs/FA309271/
I assume that this SoMachine functionality here was brought forward in the renaming to 'EcoStruxure Machine Expert'..
If there's additional loop complexity (i.e. variable number of pumps etc), then I've often found that auto-tuning can be problematic, and you really need to have some knowledge of how the PID does its magic (i.e. understanding the Proportional / Integral / Derivative terms, however they're calculated, and what things contribute to overall loop gain, and loop response).
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-04 11:22 PM
I think this article is related to machine expert basic, i was wondering if there is auto tuning mode like this mentioned in the article but with machine expert.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-05 07:00 AM
There is a autotune function for PID heating control integrated.
An other autotune is not integrated. With ESME Basic and ESME HVAC you will get an autotune function.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-12 03:56 AM
There is a autotune function for PID heating control integrated.
An other autotune is not integrated. With ESME Basic and ESME HVAC you will get an autotune function.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-12 10:25 PM
It is hidden here
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-18 02:26 PM
Thank you very much, my problem is solved.
I was using v1.3, when I updated to v2.2, I was able to load the library from where you showed. Now I can add the function block.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-21 05:34 AM
So it is working only with heating application and not applicable with pump operation?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-22 01:29 AM
Yes that is correct, but in the end I should not make a difference.
Because heating application will rise the output if the actual value is lower then the setpoint.
And in Booster pumping application the output will also rise if the actual value is lower then the setpoint.
The process of the autotune mechanisme is the same.
As alternativ you could ask ChatGPT or Copilot to creat a function for this purpose.
Here an example
FUNCTION_BLOCK FB_AutoTune_PID_ZN
VAR_INPUT
xEn : BOOL; // Enable autotuning
fSetpoint : REAL; // Setpoint in Bar
fActual : REAL; // Actual pressure in Bar
END_VAR
VAR_OUTPUT
fP : REAL; // Proportional gain
fI : REAL; // Integral time
fD : REAL; // Derivative time
END_VAR
VAR
fError : REAL;
fPrevError : REAL;
fKu : REAL; // Ultimate gain
fPu : REAL; // Oscillation period
iWaveStep : INT;
tStart : TIME;
tNow : TIME;
bOscillating : BOOL;
tLastPeak : TIME;
tCurrentPeak : TIME;
bPeakDetected : BOOL;
END_VAR
IF xEn THEN
fError := fSetpoint - fActual;
// Simulate 3 wave steps to provoke oscillation
CASE iWaveStep OF
0:
fKu := 1.0; // Initial guess
tStart := TIME(); // Start time
iWaveStep := 1;
1:
// Detect oscillation peak (simplified)
IF fError > 0.05 AND NOT bPeakDetected THEN
tLastPeak := tCurrentPeak;
tCurrentPeak := TIME();
bPeakDetected := TRUE;
IF tLastPeak > T#0s THEN
fPu := REAL_TO_TIME(TIME_TO_REAL(tCurrentPeak - tLastPeak));
iWaveStep := 2;
END_IF
ELSIF fError < 0.01 THEN
bPeakDetected := FALSE;
END_IF
2:
// Apply Ziegler-Nichols closed-loop tuning rules
fP := 0.6 * fKu;
fI := fPu / 2.0;
fD := fPu / 8.0;
iWaveStep := 3;
END_CASE
END_IF
TM241 isn´t the controller for pumping applications. Regarding to this point such a function is missing.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-25 12:33 AM
Dear Bastian,
Thanks for your support and your kind replies.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-12-01 11:52 PM
Did you try using that FB for your application? Did it work? I need an autotune PID to control a proportional valve according to the flow of a resin. So, if the flow is under the Set Point, it needs to open more the valve, and viceversa.
Thanks in advance!