EcoStruxure Operator Terminal Expert V3 dynamic objects

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

Solved
gyorgy_roland_c
Cadet
0 Likes
2
681

EcoStruxure Operator Terminal Expert V3 dynamic objects

Is it possible to create dynamic groups or contents that accept variables as parameters in EOTE? Those variables would change visibilities, or even colors of items, e.g. circuit breaker open-closed states, motor run or stop states. 

Tags (1)

Accepted Solutions
Bastian_Schmitz
Commander Commander
Commander

Re: EcoStruxure Operator Terminal Expert V3 dynamic objects

Hello Roland,

If you group several object you could change the visibility of this group via one variabel or via script.

esote group.PNG

You must only add a variabel at the visibile attribut. 

If you want to change colours globally in your project you have the possibility to work with variabels instead of constances.

esote füllung.PNG

If you use a variabel for a colour. You could use a global script which defines the value of this variabel in combination with the status of your PLC program. In that case you could easiely globaly adapt objects.

 

See Answer In Context

Tags (1)
2 Replies 2
Paul_Derbyshire
Ensign Ensign
Ensign
0 Likes
0
651

Re: EcoStruxure Operator Terminal Expert V3 dynamic objects

Hello @gyorgy_roland_c ,

 

Using EcoStruxure Operator Terminal Expert v3.2 SP1 or earlier parameters are not supported.   Instead, please use an array and change the index of the array.

 

For example, you can have 1 or more custom arrays of the items you need to work with:

 

  • MyArray[0] = PLC 1, tagname/address = Torque
  • MyArray[1] = PLC 2, tagname/address = Torque
  • MyArray[2] = PLC 1, tagname/address = Speed
  • MyArray[3] = PLC 2, tagname/address = Speed

 

Create an integer tag called, MyIndex

 

Within the switch, lamp, visibility  etc. use = MyArray[MyIndex]

 

Now when you change the value of MyIndex you can switch between different PLCs and tagnames/addresses.

 

If you require a specific project example please respond with your specific need and I can develop one for you.

Paul Derbyshire
Senior Product Application Expert | Sales Enablement | HMI Line of Business, Digital Factory | Industrial Automation Business | Schneider Electric

Bastian_Schmitz
Commander Commander
Commander

Re: EcoStruxure Operator Terminal Expert V3 dynamic objects

Hello Roland,

If you group several object you could change the visibility of this group via one variabel or via script.

esote group.PNG

You must only add a variabel at the visibile attribut. 

If you want to change colours globally in your project you have the possibility to work with variabels instead of constances.

esote füllung.PNG

If you use a variabel for a colour. You could use a global script which defines the value of this variabel in combination with the status of your PLC program. In that case you could easiely globaly adapt objects.

 