Converting an Modbus RTU protection relay (VIP410) to communicate measurements to client BMS by TCP using M221

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • Converting an Modbus RTU protection relay (VIP410) to communicate measurements to client BMS by TCP using M221
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
32
LeTomas
Lt. Commander LeTomas Lt. Commander
11
RoozeeR
Lt. Commander RoozeeR Lt. Commander
6
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
6
View All
Related Products
product field
Schneider Electric
Logic Controller - Modicon M221
product field
Schneider Electric
EcoStruxure™ Machine Expert - Basic

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Industry Automation and Control Forum
Yarom
Lieutenant JG Yarom Lieutenant JG
Lieutenant JG

Posted: ‎2024-11-11 06:32 AM

0 Likes
1
546
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-11 06:32 AM

Converting an Modbus RTU protection relay (VIP410) to communicate measurements to client BMS by TCP using M221

Hi,

 

I am almost done with the application.

 

I have a VIP410 protection relay with Modbus RTU.  I am required to convert that and data regarding switchgear states to client BMS through Modbus TCP.

 

I have an M221. I configured the digital inputs and can read their states using Doctor Modbus (or any other Modbus application).

 

I configured on the M221 Modbus RTU IO Scanner with a set of addresses.  I have 2 VIP410 units. Device ID 1 and 2.  I am able to read on the PLC both.  However, I cannot read more than just one register. I do not know what address I am supposed to read from.

 

 

 

This works. I am able to read in Machine Expert - Basic the current values on the registers I configured.

 

My question, plain and simple, what is the address that I should be reading in Doctor Modbus? I tried 100, there is nothing. I tried 1, nothing. I set both device channel details to be the same as I am to read the same registers from each device.

 

Yarom_1-1731334579364.png

 

Here is the table I am referring to from the VIP410:

 

Yarom_2-1731334727314.png

I set the channel to start with register 1024 and took 12 length for the number of registers.

 

I did the same for the Device ID 2.

 

Here is the reading by the PLC:

 

Yarom_3-1731334886542.png

 

Here is what Doctor Modbus sees:

 

Yarom_4-1731334937221.png

 

It reads the right current that I am injecting at register 1 which is (as I assume) 100.0.0 of the PLC.

 

I can I not find the one of device 2?

 

I continued with my test on device 1 and moved the injection to phase 2 of both panels. In the PLC I am able to read the phase 2 current at 100.0.1 but I cannot see it in Doctor Modbus. I am not sure of which address to read from.

 

What am I missing?

 

Thank you for the assistance.

 

Yarom

 

 

Labels
  • Labels:
  • Process Automation Talks
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2024-11-12 12:25 PM

1 Like
0
510
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-11-12 12:25 PM

Hi,

So far I see you write all values from the IO Scanner to the same %MW. Is the one value which you get correct? Did you use FC3 or FC4 in the channel configuration? Did you check to start at 1023 or 1025?

Some Devices start at Register 0 some at Register 1.

Did you check the status of the IOScanner ?

Bastian_Schmitz_0-1731443072761.png

 

And finally you could do this easier. If you only need to convert Modbus RTU into Modbus TCP you could direct use TM172SIG. This need only be to configured via webserver as Gateway and then the BMS could directly read the RTU values via TCP.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of