Posted: 2024-10-3102:03 PM
Altivar 320 Adjustable Speed Control with Digital Inputs and Potentiometer
Good afternoon, I have an Altivar 320 currently set up so that when Digital Input 1 (DI1) is activated, it starts the motor and allows control via the potentiometer with LSP = 6 Hz and MSP = 60 Hz. Now, I’ve been asked to add a function where, when Digital Input 2 (DI2) is activated, the MSP value changes to 45 Hz, allowing it to be adjustable with the potentiometer across the full range, from 6 Hz to 45 Hz. The same would apply to DI3. Any ideas? Thanks in advance.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-1812:41 PM
Good afternoon, Bastian. Thank you for your support. I made the change, and when I activate DI2, the VFD runs at 45 Hz, but it is not adjustable from the potentiometer. Thank you.