Altivar 320 Adjustable Speed Control with Digital Inputs and Potentiometer
  • Industrial Automation
  • Altivar 320 Adjustable Speed Control with Digital Inputs and Potentiometer
Bastian_Schmitz
35
LeTomas
14
JerryBartlemay
7
alexmtnz
Crewman alexmtnz
Crewman
Posted: ‎2024-10-31 02:03 PM
615
Good afternoon, I have an Altivar 320 currently set up so that when Digital Input 1 (DI1) is activated, it starts the motor and allows control via the potentiometer with LSP = 6 Hz and MSP = 60 Hz. Now, I’ve been asked to add a function where, when Digital Input 2 (DI2) is activated, the MSP value changes to 45 Hz, allowing it to be adjustable with the potentiometer across the full range, from 6 Hz to 45 Hz. The same would apply to DI3. Any ideas? Thanks in advance.
  • Process Automation Talks
Bastian_Schmitz
Admiral
Posted: ‎2024-11-04 10:25 PM
1
604
Hi check these parameters. SH2/SH4 HSP2..4
Sorry for the german text in screenshot. But with the parameter name you will find the meaning of the parameters in the manual.
alexmtnz
Crewman alexmtnz
Crewman
Posted: ‎2024-11-18 12:41 PM
In response to Bastian_Schmitz
Good afternoon, Bastian. Thank you for your support. I made the change, and when I activate DI2, the VFD runs at 45 Hz, but it is not adjustable from the potentiometer. Thank you.