Posted: 2024-08-07 04:21 AM
Hiya,
Is there a way to set the following:
LI1 - Fast Forward
LI2 - Slow Forward
LI3 - Slow Reverse
LI4 - Fast Reverse
The inputs will be from sensors so as a unit hits a sensor, it will then feed a signal to the various inputs to change the speeds.
Is this possible, or am I going about this wrong?
Thanks,
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-08-22 02:19 AM
Yes, it is possible.
Use RPS function (set to Yes, allowing ramp function commutatio) then affect to LIx.
It is possible to set Acc & ac2 with two different ramps, same for DEC and de2.
it is also possible to use preset speed if you want to assign a given speed to a LI (now we use DI as Digital input instead of Logic input this is what we use on new drives, ;-))
I hope it helps