Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-05 05:22 AM
Good morning,
I have configured the drive as follow:
Frequency referece on HMI with LCC on Fr1 parameter.
Ctrl--> to "2C"
FWD command to DI1
rrS command to DI2
If I set the frequency manually on the Inveter with the handle, and rise to 24V DI1 the inverter doesn't start the motor.
All the COM reference is a 0V, and te dip switch are on Source and DI6.
Any advice?
Thank you
Best regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-06 02:35 AM
I found the solution.
Parameter
CHCF to SEP
Fr1 to AIU1
Bye
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.