Good morning,
I have configured the drive as follow:
Frequency referece on HMI with LCC on Fr1 parameter.
Ctrl--> to "2C"
FWD command to DI1
rrS command to DI2
If I set the frequency manually on the Inveter with the handle, and rise to 24V DI1 the inverter doesn't start the motor.
All the COM reference is a 0V, and te dip switch are on Source and DI6.
Any advice?
Thank you
Best regards
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-03-06 02:35 AM
I found the solution.
Parameter
CHCF to SEP
Fr1 to AIU1
Bye
Link copied. Please paste this link to share this article on your social media post.