ATV320 Modbus communication or serial communication parameter write issue?
  • Industrial Automation
  • ATV320 Modbus communication or serial communication parameter write issue?
Bastian_Schmitz
35
LeTomas
14
JerryBartlemay
7
Sattu_98
Crewman Sattu_98
Crewman
Posted: ‎2024-06-18 03:21 AM . Last Modified: ‎2024-06-18 03:24 AM
1
761
I am using ATV320 drive and using on terminal mode operation. I am changing  the parameter through Modbus poll or Modbus scan software. I am changing the values of parameter through software(Modpoll or Mod scan), we are able to see changes in drive, but when I do power cycle (Turn drive off and on) then value are getting changed in drive, it will retain its original value it will not show the changed values. What can be the reason of this?
Below are the parameter I am trying to change through Modbus poll or Modbus scan.
Sr no LAC Address Label Default
1 FRS 9602 Nominal motor Frequency 50Hz
2 ACC 9001 Acceleration ramp time 3s
3 LSP 3105 Low speed 0 Hz
4 HSP 3104 High speed 50 Hz
5 CRL3 4434 AI3 Current Scaling parameter of 0% 0 mA
6 R2 5002 R2 assignment Not assigned
7 AO1 5021 AQ1 Assigment Not Configured
8 AOL1 4641 AQ1 min Output value 0 mA
9 RSF 7124 Fault reset input assigment Not assigned
10 R1 5001 R1 Assignment Device Running
  • Smart Operations
  • ATV320 Drive
  • Modbus Communication
  • modpoll
Bastian_Schmitz
Admiral
Posted: ‎2024-06-18 06:08 AM
you need to write the values to eeprom