ITA System requirements
EcoStruxure IT Advisor system requirements for on-premises installations
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
ITA 9.1.1 and newer supports installation on RHEL 8.x and Rocky Linux 8.x
RHEL 9 is not yet supported.
Installing ITA 9.1.0 on a Red Hat operating system is not supported.
IMPORTANT: To install ITA 9.1.x on VMware, plan to use VMware ESXi 6.5 U1 or newer. Otherwise, you may see a kernel bug error in CentOS 8.x. See VMware KB article https://kb.vmware.com/s/article/2151480 for more information.
These system specifications are recommendations for your IT Advisor system configuration in general. The performance and operation of the system depends largely on the nature of the configuration, such as:
Number and population of racks
Number and nature of integrations to external systems
Number of devices and number of data points stored on these
Power path configuration (one big, several small, across rooms, etc.)
Concurrent and total users of the system and nature of their work cycle
If ITA is running on lower specification servers than recommended, users may experience long response times or timeout issues. In addition, the server may not be able to process scheduled jobs in a timely manner.
Recommended server hardware for IT Advisor on-premises
ITA on-premises requires a dedicated server, either hardware or a virtual environment. The operating system is included in the installation.
Recommended IT Advisor server configuration
Server requirement guidelines (minimum)
CPU: 4 cores minimum. We recommend 8 cores
Memory: 16 GB RAM (absolute minimum requirement)
200 GB storage, speed minimum 170 MB/s
Disaster recovery network: 10 Mbps with low latency <100 ms
Note: If you're installing ITA on-premises on an existing server, note that ITA claims almost all memory (JVM about 8 GB and Postgres about 6 GB alone). You might experience issues if you have other applications running on the server, such as surveillance and monitoring agents.
Server requirement guidelines for 10,000 racks across 200 rooms with 30 concurrent users
8 CPU cores
32 GB RAM
200 GB storage, speed minimum 170 MB/s
Server requirement guidelines for 20,000 racks across 400 rooms with 30 concurrent users
16 CPU cores
64 GB RAM
200 GB storage, speed minimum 170 MB/s
RAID systems
Hardware RAID controllers are recommended. We tested hardware controllers in the DELL x20 series, IBM M4 series, and HP G8 series. Be aware there might be hardware RAID controllers that we have not tested in special configurations.
Not supported:
Generally all software RAID controllers
HP RAID Controller B-Series
DELL RAID Controller S-Series
Security configuration
For information about security configuration, see here.
IT Advisor server communication
For information on server communication, see here.
Recommended IT Advisor desktop client configuration
For minimum recommendations for running ITA, see here.
You must have local administration rights on the client computer during installation, first login, and license upgrade.