ITA system requirements for on-premises installations

ITA System requirements

EcoStruxure IT Advisor system requirements for on-premises installations

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • IT Advisor
  • ITA System requirements
  • ITA system requirements for on-premises installations
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • ITA system requirements for on-premises installati...
  • ITA system requirements for on-premises installati...

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to ITA System requirements
Start a Topic
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
10539 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

ITA system requirements for on-premises installations

Picard EcoStruxureIT
‎2019-10-24 01:01 AM

Last Updated: Admiral Jef Admiral ‎2024-11-29 06:08 AM

ITA 9.1.1 and newer supports installation on RHEL 8.x and Rocky Linux 8.x

RHEL 9 is not yet supported.

Installing ITA 9.1.0 on a Red Hat operating system is not supported.

 

IMPORTANT: To install ITA 9.1.x on VMware, plan to use VMware ESXi 6.5 U1 or newer. Otherwise, you may see a kernel bug error in CentOS 8.x.
See VMware KB article https://kb.vmware.com/s/article/2151480 for more information.

 

These system specifications are recommendations for your IT Advisor system configuration in general. The performance and operation of the system depends largely on the nature of the configuration, such as: 

 

  • Number and population of racks
  • Number and nature of integrations to external systems
  • Number of devices and number of data points stored on these
  • Power path configuration (one big, several small, across rooms, etc.)
  • Concurrent and total users of the system and nature of their work cycle

 

If ITA is running on lower specification servers than recommended, users may experience long response times or timeout issues. In addition, the server may not be able to process scheduled jobs in a timely manner. 

 

Recommended server hardware for IT Advisor on-premises

 

ITA on-premises requires a dedicated server, either hardware or a virtual environment. The operating system is included in the installation.

 

Recommended IT Advisor server configuration

 

Server requirement guidelines (minimum)

 

  • CPU: 4 cores minimum. We recommend 8 cores
  • Memory: 16 GB RAM (absolute minimum requirement)
  • 200 GB storage, speed minimum 170 MB/s
  • Disaster recovery network: 10 Mbps with low latency <100 ms 

 

Note: If you're installing ITA on-premises on an existing server, note that ITA claims almost all memory (JVM about 8 GB and Postgres about 6 GB alone). You might experience issues if you have other applications running on the server, such as surveillance and monitoring agents.

 

Server requirement guidelines for 10,000 racks across 200 rooms with 30 concurrent users

 

  • 8 CPU cores
  • 32 GB RAM
  • 200 GB storage, speed minimum 170 MB/s

 

Server requirement guidelines for 20,000 racks across 400 rooms with 30 concurrent users

 

  • 16 CPU cores
  • 64 GB RAM
  • 200 GB storage, speed minimum 170 MB/s

 

RAID systems

 

Hardware RAID controllers are recommended. We tested hardware controllers in the DELL x20 series, IBM M4 series, and HP G8 series. Be aware there might be hardware RAID controllers that we have not tested in special configurations.

 

Not supported:

 

  • Generally all software RAID controllers
  • HP RAID Controller B-Series
  • DELL RAID Controller S-Series

 

Security configuration

 

For information about security configuration, see here.

 

IT Advisor server communication

 

For information on server communication, see here.

 

Recommended IT Advisor desktop client configuration

 

For minimum recommendations for running ITA, see here. 

 

You must have local administration rights on the client computer during installation, first login, and license upgrade.

 

 

Was this article helpful? Yes No
50% helpful (1/2)

Link copied. Please paste this link to share this article on your social media post.

Comments
JMollica
JMollica Cadet
Cadet
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2025-04-29 09:43 AM

Hi, just a note to please mention that the 'root' directory should have 200GB minimum allocation, in addition to other hard drive disk partition storage.

 

Thank you 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore