Installing IT Optimize

ITA: IT Optimize (on-premises only)

EcoStruxure IT Advisor: IT Optimize (on-premises deployments only) provides insight into the IT layer of the data center through integration with external IT systems.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • IT Advisor
  • ITA desktop client
  • ITA: IT Optimize (on-premises only)
  • Installing IT Optimize
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • Announcement: IT Optimize discontinued
  • Installing IT Optimize
  • Configuring IT Optimize server integration
  • Configuring IT asset discovery
  • Configuring HPUX, Solaris, and AIX discovery
  • Underutilized Servers report
  • Server Utilization report
  • Server Power Consumption report
  • Announcement: IT Optimize discontinued
  • Installing IT Optimize
  • Configuring IT Optimize server integration
  • Configuring IT asset discovery
  • Configuring HPUX, Solaris, and AIX discovery
  • Underutilized Servers report
  • Server Utilization report
  • Server Power Consumption report

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to ITA: IT Optimize (on-premises only)
Start a Topic
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
3475 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Installing IT Optimize

Picard EcoStruxureIT
‎2020-08-03 03:17 AM

Download the IT Optimize installation zip file from a location provided by your local technical support team. There are installers for both Linux 64-bit and Windows 64-bit.

The DCO or IT Advisor server must have IT Optimize licenses installed. ITO licenses are also rack based, so you need the same amount of ITO licenses as the installed ITA base license.

IT Optimize is compatible with DCO 8.x and all versions of IT Advisor 9.x.

Installing ITO on Windows

IT Optimize Windows Server minimum requirements

  • 2 CPUs
  • 4GB RAM
  • A minimum of 20GB of free disk space on the disk where ITO will be installed
  • Windows 2012, 2012 R2, 2016 and 2019
    Windows 2008 and 2008 R2 should still work but are no longer tested and qualified.

Instructions

  1. Download the IT Optimize installer zip file for windows and place it in a temporary folder on the windows IT Optimize server.

  2. Open the folder in which the downloaded zip file was placed and extract the contents of the StruxureWareItOptimizeWithServerAccess-setup-7.5.x.windows.x64.zip file to a temporary folder.

  3. Change to the folder to which the zip file was extracted. The folder for ITO 7.5.x will contain the following files. The StruxureWareItOptimize-setup.windows.x64.exe is the installer file which will be executed.
    DO NOT run any of the other “bat” or “exe” files in this folder as it may lead to unexpected results.

    ITO_Windows_1_360011650218.pngITO_Windows_1_360011650218.png

  4. Double-click the StruxureWareItOptimize-setup.windows.x64.exe file and follow the instructions in the wizard to complete installation:

  • Choose the language and click OK.

    ITO_Windows_2_360011650218.pngITO_Windows_2_360011650218.png

  • Click Next > to continue.

    ITO_Windows_3_360011650218.pngITO_Windows_3_360011650218.png

  • Set the installation directory and default port used by DCO or IT Advisor to access the IT Optimize server.
    Default installation folder is C:\Program Files\Schneider-Electric\ITOptimize
    Default IT Optimize port is 8090. (This port may need to be opened in Windows firewall to allow connections from DCO or ITA.)

    ITO_Windows_4_360011650218.pngITO_Windows_4_360011650218.png

  • Click Next > to continue. If the IT Optimize server has less than 20GB of free disk space on the target installation directory, then a warning will appear.

    ITO_Windows_5_360011650218.pngITO_Windows_5_360011650218.png

  • Enter the credentials for the Windows user account which will run the IT Optimize service. This user account must be a valid local or domain based Windows user with local administrator rights and the account must belong to the Logon as a Service role.

    To see how to enable the user to "logon as a service": http://technet.microsoft.com/en-us/library/cc794944(v=ws.10).aspx)

    ITO_Windows_6_360011650218.pngITO_Windows_6_360011650218.png

    If a domain-based user account is specified in the above window, the installer will pop-up a window stating it would like to test the user accounts security before proceeding. Follow those directions to complete the test which confirms the domain-based user account has the Logon as a Service privilege.

  • Click Next > to continue.

  • Accept the default port (3306) used by the IT Optimize service to connect to its local database which is also installed.

    ITO_Windows_7_360011650218.pngITO_Windows_7_360011650218.png

  • Click Next >

    ITO_Windows_8_360011650218.pngITO_Windows_8_360011650218.png

  • Click Next > to begin the installation.

  • Wait for the installation to complete. The installation may take several minutes.

  • The IT Optimize installer will also install Intel’s Data Center Manager (DCM) and Virtual KVM software on the ITO server. Their installers are automatically started by the ITO installer. There is no need to try to install either of them yourself.

  • When completed, the popup window will ask whether to start ITO services now. Leave this item checked and click “Finish” to complete installation.

    ITO_Windows_9_360011650218.pngITO_Windows_9_360011650218.png


    The “Programs and Features” view in Control Panel should now have the following three entries (the versions may differ depending on the IT Optimize release).

    ITO_Windows_10_360011650218.pngITO_Windows_10_360011650218.png

  • Verify the installation and connectivity.
    To confirm the IT Optimize services are running, open a browser on the IT Optimize server and try to browse to https://localhost:8090
    If the IT Optimize services are running, the following logon window should appear. You can logon using apc/apc credentials.

    ITO_Windows_11_360011650218.pngITO_Windows_11_360011650218.png

    To access the above logon from a system external to the IT Optimize server, you may need to add port 8090 as an allowed incoming TCP port in windows firewall. This port is used by DCO and/or IT Advisor for IT Optimize integrations.
  • Installing ITO on Linux

    IT Optimize Linux minimum server requirements

    2 CPUs

    4GB RAM

    A minimum of 20GB of free disk space on the disk where ITO will be installed

    CentOS 7.x and RedHat 7.x are supported.
    Most other Linux OS’s will work but the below prerequisites and firewall commands may change.

    Prerequisite Linux modules

    lsb

    unzip

    net-tools

    # yum install lsb unzip net-tools

    Instructions

    1. Download the IT Optimize installer tar.gz file for Linux and place it in a temporary folder on the IT Optimize server, like /var/tmp.

    2. Log on to the ITO server. Change to the folder where the downloaded tar.gz file was placed and extract the contents of StruxureWareItOptimizeWithServerAccess-setup-7.5.x.linux.x64.tar.gz. DO NOT run any of the “.sh” files in this folder as it may lead to unexpected results.

    # tar xvzf StruxureWareItOptimizeWithServerAccess-setup-7.5.x.linux.x64.tar.gz

    # ls -lt

    total 1902480

    -rwxr-xr-x. 1 root root 970393722 Apr 24 11:37 StruxureWareItOptimizeWithServerAccess-setup-7.5.x.linux.x64.tar.gz

    -rwxr-xr-x. 1 root root      6501 Nov 27 18:56 intel_vGateway_install64.sh

    -rwxr-xr-x. 1 root root      7881 Nov 27 18:56 intel_install64.sh

    -rwxr-xr-x. 1 root root       563 Oct 16  2018 install_dcm.sh

    -rwxr-xr-x. 1 root root       325 Oct 16  2018 install_vGateway.sh

    -rwxr-xr-x. 1 root root 181723501 Oct 16  2018 Intel(R)_Virtual_Gateway64_1_4.tar.gz

    -rwxr-xr-x. 1 root root 301674987 Oct 16  2018 StruxureWareItOptimize-setup.linux.x64.bin

    -rwxr-xr-x. 1 root root 172810387 Oct 16  2018 Intel(R)_Data_Center_Manager64_upgrade_4_2.tar.gz

    -rwxr-xr-x. 1 root root 149356963 Oct 16  2018 Intel(R)_Data_Center_Manager64_upgrade_4_1.tar.gz

    -rwxr-xr-x. 1 root root 172138128 Oct 16  2018 Intel(R)_Data_Center_Manager64_4_2.tar.gz

    Change the permissions on the ITO installer and shell files to be executable. If this step is skipped the Intel DCM products will not be installed. Go to the temp folder in which the ITO installer zip was extracted.

    # chmod 755 *.bin *.sh

    Run the IT Optimize installer and answer the installer questions as needed.

    # ./StruxureWareItOptimize-setup.linux.x64.bin

    Once completed, it may be necessary to open port 8090 on the ITO server if the Linux firewall is active.

    To verify whether the firewall is running, run the command firewall-cmd –state to see if it returns running.

    # firewall-cmd --state
    running

    Verify which firewall zone is active

    # firewall-cmd  --get-active-zones

    public

         interfaces: ens192

    Add port 8090 to the running and permanent firewall rules. Substitute the proper "active" firewall zone if "public" is not correct. Also substitute "8090" with the customized port id if this port number was changed during ITO installation.

    # firewall-cmd --zone=public --add-port=8090/tcp
    # firewall-cmd --zone=public --permanent --add-port=8090/tcp

     You should be able to access to the ITO server by browsing to https://<ITO-Server-IP>:8090/

     

    Was this article helpful? Yes No
    No ratings

    Link copied. Please paste this link to share this article on your social media post.

    You’ve reached the end of your document

    WHAT’S NEXT?

    Ask our Experts

    Didn't find what you are looking for? Ask our experts!

    My Dashboard

    Check out the new Feeds and activities that are relevant to you.

    To The Top!

    Forums

    • APC UPS Data Center Backup Solutions
    • EcoStruxure IT
    • EcoStruxure Geo SCADA Expert
    • Metering & Power Quality
    • Schneider Electric Wiser

    Knowledge Center

    Events & webinars

    Ideas

    Blogs

    Get Started

    • Ask the Community
    • Community Guidelines
    • Community User Guide
    • How-To & Best Practice
    • Experts Leaderboard
    • Contact Support

      Ask our Experts

      Have a question related to our products, solutions or services? Get quick support on community Forums

      Email Us

      For Community platform-related support, please email us

    Brand-Logo
    Subscribing is a smart move!
    You can subscribe to this board after you log in or create your free account.
    Forum-Icon

    Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

    Register today for FREE

    Register Now

    Already have an account? Login

    Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

    Welcome!

    Welcome to your new personalized space.

    of

    Explore