EcoStruxure IT Advisor: IT Optimize (on-premises deployments only) provides insight into the IT layer of the data center through integration with external IT systems.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Configure user credentials to allow EcoStruxure IT Advisor on-premiseto communicate with the IT Optimize serverand receive device data and alarms.
Set up the server connection inIT Advisor.
SelectSystem Setup > External System Configuration.
ClickAdd server, and selectIT Optimize serveras the server type.
Type theIT Optimize serverinformation, host name and IP address.
ClickTestto test the connection.
You can integrate with multipleIT Optimize servers.
ThePolling intervaloption is a setting relevant for data on theIT Optimize serveronly. It defines how often theIT Optimize serverrequests CPU utilization data from the devices.
There is no setting defining how oftenIT Advisorrequests data from theIT Optimize server. These are predefined: power and CPU utilization data every 10 seconds; new or changes to devices every 60 seconds.
ITA_external_system_ITO_cascade_360011539637.png
Workaround for ITO failed discovery of the IT Advisor server
WARNING!This operation will reduce security on the Data Center Operation server.
On theData Center Operationserver, to work around the security restrictions preventing ITO discovery:
Log on to the server with an SSH client. For example, use PuTTY. You can download it fromhere.
Type the commandsudo sed -i -e "s/^#%sudo/%sudo/g" /etc/sudoers.d/itodiscoveryand click Enter.
If you reinstall or upgrade the server, you must perform the above procedure again.