Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

turbine/rotor flow sensor

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • turbine/rotor flow sensor
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
FedericoM Mentor
119
Bastian_Schmitz
Bastian_Schmitz Champion
64
M_Cervati
M_Cervati Troubleshooter
18
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Related Products
product field
Schneider Electric
EcoStruxure™ Machine Expert - HVAC

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to HVAC and Pumping Forum
Start a Topic
Solved
otrotabi
otrotabi
Contributor

Posted: ‎2022-10-27 08:22 AM

0 Likes
5
2432
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-27 08:22 AM

turbine/rotor flow sensor

I would like to use a turbine/rotor type flow sensor. It consists of a magnet which is mounted on top of the rotor and a Hall effect sensor placed on top of the rotor.

 

The model I am looking will generate a square wave output signal with a frequency (hz) = 6 x flow (lts/min) and a maximum flow of 50 lts/min, so that should give us a maximum 300 hz square wave input.

 

I could use either TM171 (preferably) of TM172 if needed.

 

I have done something similar in the past with the help of @LeTomas. What we did  was to input the rotor flow directly to an analog input and hopefully the RC characteristics of the input gives a dc value which is related to the input frequency/flow.

 

So basically my question is: is there a different approach I could use ? Could I count pulses with a Rtrig for example ? I guess not because 1/300 = 3.3 msec which is far less than 100 msec scan time but I am a little lost.

 

 

Labels
  • Labels:
  • HVAC
  • Tags:
  • ecostruxure
  • english
  • hvac
  • TM171
  • TM172
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
FedericoM
FedericoM Mentor
Mentor

Posted: ‎2022-10-27 08:29 AM

0 Likes
4
2428
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-27 08:29 AM

The right solution should be the 24Vdc fast digital input of TM172, it counts pulses and provide frequency of the last period.

What you did in the past with M171 might work also in this case, but I guess with a lower accuracy,

 

If you want just to detect if there are pulses or not (flow alarm), SmartBios lib allows to read DI status both on background and timed, combining this with a debounce reduced to 0 on the DI. If this is the case M171 could be enough...

See Answer In Context

  • Tags:
  • english
  • TM171O
  • TM172
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
FedericoM
FedericoM Mentor
Mentor

Posted: ‎2022-10-27 08:29 AM

0 Likes
4
2429
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-27 08:29 AM

The right solution should be the 24Vdc fast digital input of TM172, it counts pulses and provide frequency of the last period.

What you did in the past with M171 might work also in this case, but I guess with a lower accuracy,

 

If you want just to detect if there are pulses or not (flow alarm), SmartBios lib allows to read DI status both on background and timed, combining this with a debounce reduced to 0 on the DI. If this is the case M171 could be enough...

  • Tags:
  • english
  • TM171O
  • TM172
Reply

Link copied. Please paste this link to share this article on your social media post.

otrotabi
otrotabi
Contributor

Posted: ‎2022-10-27 09:58 AM . Last Modified: ‎2022-10-27 09:59 AM

In response to FedericoM
0 Likes
3
2419
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-27 09:58 AM . Last Modified: ‎2022-10-27 09:59 AM

I will probably end up using a TM172 (or eventually a dedicated square wave to dc board should I need to use TM171) but you have made me curious and I would like to learn something new 🙄.

 

I guess the SmartAsyncDI is the FB you refer to.

smartasynv.jpg

What does it mean that it runs asynchronous from timed task ? Where should I place this FB ? 

 

In any case, go/no go is not what I am looking for (particularly because you may get a 1 if there´s no flow in case the magnet is placed under the hall effect sensor) but also since I would like to stop the chiller if flow gets below a certain flow. In any case I am not trying to implement a good flowmeter here.

 

I would also be willing to try other suggestions if I can get away from paddle switches which are hard to set up correctly.

 

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Bastian_Schmitz Champion
Champion

Posted: ‎2022-10-27 10:03 AM

In response to otrotabi
0 Likes
2
2415
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-27 10:03 AM

Which typ of Flow switch did you use? The turbin sensors from SIKA with NPN output work proper an DI1 or DI2. But in that case you need to connect the NPN output to COM_DI of CN3 and 24V+ constant signal on DI1 or DI2. In that case you lost one Digital Input.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Bastian_Schmitz Champion
Champion

Posted: ‎2022-10-27 10:05 AM

In response to Bastian_Schmitz
0 Likes
0
2413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-27 10:05 AM

Or you could use a Vortx sensor with analog output like these Link

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

otrotabi
otrotabi
Contributor

Posted: ‎2022-10-27 11:04 AM

In response to Bastian_Schmitz
0 Likes
0
2406
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-10-27 11:04 AM

I am afraid I do not get them here from Sika, at least not from stock. Looks like a fine solution. I will try to find out if there are any distributors.

 

This is what I get here. I´ve tried a similar plastic case version and they work fine for a long time (or until they break, whatever happens first 😁). Seriously, they seem to work. Probably Sika has included an op amp and some other stuff to count pulses and give you a DC output with the same principle. We are trying to get away from paddle type switches.

 

 

yfb10.jpg

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore