The TM172PDG42RI 42 I/O PLC is not polled using the Modbus RTU protocol (RS485-1 and RS485-2 ports)

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • The TM172PDG42RI 42 I/O PLC is not polled using the Modbus RTU protocol (RS485-1 and RS485-2 ports)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
Captain FedericoM Captain
93
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
56
M_Cervati
M_Cervati Support
15
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to HVAC and Pumping Forum
Start a Topic
Solved
viy-777
Crewman viy-777
Crewman

Posted: ‎2025-10-31 10:44 PM

0 Likes
2
164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-10-31 10:44 PM

The TM172PDG42RI 42 I/O PLC is not polled using the Modbus RTU protocol (RS485-1 and RS485-2 ports)

Hello! The task is to poll the PLC using the Modbus RTU protocol (by RS485-2).
All the necessary settings have been made:
1. In the Configuration for RS485-2, the mode was set to "Modbus Slave-BACnet MS/TP"
2. In "Commissioning", I set the type to "Modbus", the device address, and the parameters (8n1)
3. Full compilation, full load, reloaded the PLC, disconnected the USB
The survey should be carried out according to the operator panel by project. I connected for testing with a USB-RS converter. I started the "Scanner RTU" and found the device.
I started the OPC server, but there is no register survey (error: cannot open the COM port).
Please advise on a solution to this problem. Is this what I'm doing?
P.S.: I used both version 1.4.0 and 1.6.0. I updated the firmware to 596.14 (the PLC had 596.12).

 

Attachments
Labels
  • Labels:
  • HVAC
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
viy-777
Crewman viy-777
Crewman

Posted: ‎2025-11-04 07:10 PM

0 Likes
0
139
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-04 07:10 PM

It worked. The converter driver was installed incorrectly on the PC.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
M_Cervati
M_Cervati Support
Support

Posted: ‎2025-11-03 06:56 AM

0 Likes
0
163
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-03 06:56 AM

Hi,

it seems all ok, but I didn't see the COM port selected in the modcan32. Is it COM6?

If you try to use RS-485-1 with the same settings the result is the same?

 

Thank you

 

Marco Cervati

Reply

Link copied. Please paste this link to share this article on your social media post.

viy-777
Crewman viy-777
Crewman

Posted: ‎2025-11-04 07:10 PM

0 Likes
0
140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-11-04 07:10 PM

It worked. The converter driver was installed incorrectly on the PC.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore